weil-mcclain steamer
keith_27
Member Posts: 64
anything in the codes stating that the header has to be welded ?? replacing this weil-mcclain boiler about 21 years old. The present header is 3 " pipe and welded. ??
Nope
and if someone tells you they can't install 3-inch threaded pipe, find someone else. We do it all the time and it's not rocket science.
What model W-M is this? What's going to replace it?All Steamed Up, Inc.
Consulting0 -
This boiler has a 3-inch header
Not a W-M, but you get the idea:
http://www.heatinghelp.com/forum-thread/146210/This-Weeks-Steamer-Replacement
Replace that header. I'm surprised the old boiler lasted that long with a welded yoke like that.All Steamed Up, Inc.
Consulting0 -
Keith have you sized the system?
are you sure this is the boiler the system requires? As of late I have seen boilers both over and undersized so I had to ask.Cost is what you spend , value is what you get.
cell # 413-841-6726
have you looked at a wet base boiler?
if you use a wetbase boiler with a power burner you can squeeze more saving out when running the boiler.Cost is what you spend , value is what you get.
cell # 413-841-6726
There is 2": baseboard elements in two shop bays and six unit heaters in the busniess at different areas. Sized the elements and unit heaters and did find that the btu,s of the boiler is a tad short. The mechanics in the shop do keep the heat set back and the owner has been happy with what has been in there for the past 20 years.0 -
How short
is "a tad short"?0 -
The sizing is more off if the rooms are not kept at 70
Steam required goes higher per EDR as the room temperature goes down. Too small of a boiler will waste fuel with extended run times for heat. Are the units individually controlled for temperature?Cost is what you spend , value is what you get.
cell # 413-841-6726
Its a two zone system. The shop area and the unit heaters.. About 10,000 btu short. It does have another boiler that takes care of the office,break area and the owners office. It is a rental store and there have been cases of no power and heat breakdowns in which the owner used the propane heaters.0 -
If it is zoned
then being undersized is not that big of a deal.Cost is what you spend , value is what you get.
cell # 413-841-6726
I was wondering about that
The combination of pickup factor and zone diversity should change the math somehow. Is there a recipe?0