Mixing 3/4 and 1/2 inch pipe on a hot water system?
JoeDoh
Member Posts: 6
Two questions if i may about my hot water radiator system
1. First floor mud room radiator has 1/2 inch while all others in house have 3/4 inch.
Meaning, a 3/4 to 1/2 reducer has been installed in basement plumbing leading
to the mudroom radiator.
Could that impact overall system performance?
Could that impact mud room radiator performance / efficiency?
The mud room gets very cold but I attribute that to poor insulation in that room.
We are installing insulation and under floor heat mats soon
2. Second floor hotter than first floor. (as much as 6 or 7 degrees)
Have tried adjusting 2nd floor valves with minimal success.
We have no door leading to 2nd floor so that solution is out.
Am thinking first floor insulation issues causing thermostat to trigger boiler
longer thereby making 2nd floor hotter.
My guess anyway but very much appreciate your thoughts
Thanks
Joe
Thanks
Joe
Addl info..
Boiler is Weil Mclain Model CG0 -
As usual, it depends
are the radiators piped in, parallel, series, or some combination of the two? Any diverter tees?0 -
Follow up
Believe it is parallel.
Assume way to determine if serial is to shut off valve to one rad and see if others are impacted, right?
No idea what "piped in" means...
Would a pic of boiler and plumbing around provide any help ?0 -
If you could post photos
of the boiler and surrounding pipes, valves, and such plus a radiator or two with their associated valve(s) and pipes it will help a lot. Even better if you can show us where the pipes entering and leaving a radiator join the system mains.0 -
Back To Basics
Your chasing a ghost without doing a room by room heat loss, calculating each radiators capable btu/hr out put at a specific water temp and comparing that to each room's heat loss.
I have tons of rad's on 3/8" pex so highly doubt it's pipe size.There was an error rendering this rich post.
Pics
Coming off boiler the feed splits into 2. (see Boiler_two pic)
Thinking feed on right is for first floor with left feed being for 2nd floor.
About 8 feet off boiler and before hitting any rads
convert to 1/2 inch (see to_half.pic)
Approx 24 foot run to mud room rad with 1/2 inch (see to_rad).
Note on boiler says return pipes have tape as seen in to_rad pic
Out of mud room rad convert back to 3/4 feeding other 1st floor rads
(see back to 3/4 pic)
Return at boiler (see Return_to_boiler)
MANY....many thanks for your input
UPDATE after posting... darn, thought it would add them as attachments with names.
Hopefully my narrative will help with pics?0 -
Back to basics...thanks
thank you for your response.
excellent comment but at this point was looking for help in basic hot water system plumbing, if you will, around "mixing 1/2 and 3/4"....
our handyman dude pointed out the 1/2 inch into the mudroom rads
whereas all other rads had 3/4. he suggested we may need to replace all of
that 1/2 inch piping with 3/4 but I am not sure of value add of that.
he confesses to not being a hot water system expert
hence...i reached out to this forum.0 -
Heat loss
Like Chris said first step.
Then determine if there is enough base board in each room to cover the heat loss in each room. So you will need to know type of base board, and its output per Lin. Foot at its rated water temp.
Like Chris said 1/2" , 3/8". Can do the job if it can carry the btus needed for the space.
1/2" can carry 15000 btus depending on gpm which is quite a bit for a mud room.
3/8" can carry 7500 btus
3/4" can carry 40,000 btus at 4gpm0 -
Pipe Size
Is just a highway that carries btu/hr at a particular flow rate. I have 1/2" pipe running to and from my entire first floor baseboard and it's 3/4" High Capacity. Running 160 at my design day temp and heats the entire 1,200 sqft to a 70 degree set point just fine.
Your chasing a ghost without a room by room heat loss and emitter measurement for capable btu/hr ouput at a 180 degree water temp. From that you can then determined the proper pipe size needed. To calculate gpm needed to move the required btu/hr the formula is:
gpm = btu/hr divided by (delta-t x 500)
Delta-T is the temp difference between the boiler supply water temp and the returning water temp from the zone. A typical heating system is designed for a 20 degree delta-t. So, if the heat loss of a particular zone was 10,000 btu/hr you would need to move 1gpm of flow through that zone. 1/2" pipe would do the job..There was an error rendering this rich post.
- 86.7K THE MAIN WALL
- 56 Biomass
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 69 Pipe Deterioration
- 947 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes