rheem warm air furnace
Paul S_3
Paul S_3 Member Posts: 1,291
I have another problem with burners not lighting fully across...brand new them two stage furnace...only one burner lights...the one closest to the spark igniter...they light full across when I blow the gas around when its trying to light....I checked incoming gas pressure I'm getting 6.8" wc....on the outlet I'm getting .40"wc reading on both high and low fire...cannot adjust both high and low regulator on gas valve....I screw the set screw all the way down and up on both high and low regulator with no change in pressure and visible firing rate....faulty gas valve???
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Paul S_3
    model and serial
    Rheem......model # rgpe-10ebrmr.....serial#gz5d301f391204792
    347-692-4777
    ASMHVACNYC.COM
  • JStar
    JStar Member Posts: 2,752
    Gas
    Were you getting 6.8 in when the valve was open, or only static?
  • Paul S_3
    6.8"wc
    With valve open
    347-692-4777
    ASMHVACNYC.COM
  • JStar
    Rheem
    Sounds like the valve. I would try to send 24v right to it first. Could also be a low amp draw on the valve circuit, which might lead to a faulty control board.
  • heatpro02920
    heatpro02920 Member Posts: 991
    Did you
    call Rheem tech support? Sounds like a gas valve, is this a natural draft installation?
  • John Mills_5
    John Mills_5 Member Posts: 952
    I seem to recall
    hearing of manufacturing oil in the burners block the crossover. Try washing out the burners.
  • unclejohn
    unclejohn Member Posts: 1,833
    Is this the set screw
    Adjustment that has a 2mm set screw inside a 3mm set screw? If it is you need to replace the valve and If you ever find the guy that dreamed that up, kick him in the butt.