What size pex ?
Options
Heeltee
Posts: 20
I am replacing 3/4 copper base borad & copper pipe with cast iron radiators and pex . 5/8 or 3/4 ? I want to say with 3/4. Any suggestions
0
Comments
-
Depends
On the btus, and flow rates required for the emitters to satisfy the load.
You changed base board styles. Are you putting back the same amount of output as you removed?
Was there insulation upgrades to the home since tha original baseboard?
The bigger the supply pipe the less head, and smaller pump needed.0 -
3/4
A smaller pipe = more head (pressure) loss = less pressure to move the water = less heat. Go with the 3/4 pipe. If you're using pex be sure to get the pex with the oxygen barrier, slightly more expensive but absolutely worth it. Just btw, I'm wondering if you're system is hot water or steam and why you decided to switch out the copper baseboards for iron radiators?
I'm using Slant/Fin Multipak 80, 730BTUh / linear foot @ 180 degree F.0 -
Gotta do the math
Bobbito,
You have no idea what btus are needed for the heatloss. How long the loops are etc. So how do you know 3/4" pex will work? Yes he's replacing 3/4" copper.0
This discussion has been closed.
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements