Pressure rising to 60psi
Steve Garson_2
Member Posts: 712
I had to replace a leaking expansion tank last week on a radiant heating system. I installed a new one with a 20psi charge and charged the system to 20psi. The water-feed valve was then shut off.
A few days later, I saw the pressure gauge reading of 60psi. Puzzled, I drained around 2+ quarts of water and the pressure went back down to 20psi.
Today, the pressure was high again, so I drained some more. The water temp varies from 100* to 140*.
This all seems wrong. What is happening here?
Thanks,
Steve Garson
Boston, MA
Thanks,
Steve Garson
Boston, MA
Steve from Denver, CO
Leaks:
There's a leak from the high pressure (Potable, Street) side to the lower pressure, closed heating side somewhere. A indirect coil most likely.0 -
Relief valve
On top of what Ice said, that relief valve shoud have never let the boiler get above 30 psi (unless it is a rare system that is rated higher). Check the relief valve as well.
Rob0 -
Leak
That makes a lot of sense. This is my second Combicore. It is perhaps five years old. I wish my contractor installed a small boiler, instead. Any suggestions on the smallest boiler available>
SteveSteve from Denver, CO0 -
Leak
No relief
Just noticed...no relief valve on heating loop. Only on potable hot water side. Unbelievable!Steve from Denver, CO0 -
No relief
No relief
No relief
No relief
No relief
No relief
No relief
- 167 Indoor-Air Quality
