Boiler Sizing Question
We entered a bid for replacement of steam boiler.
We performed the EDR calculation.
After measuring the radiators, we calculated they measured 517 sq. ft.
The customer is requesting only a Weil-McLain SGO boiler.
Which is fine by us.
We will be installing it using a drop header, of course.
The 2 other bids they customer received both displayed SG0-4 boilers.
We recommended an SG0-5, based on our calculations, which were done twice (by 2 different people just to make sure- a kind of fail safe)
The SG0-4 has a rating of 450 sq.ft. steam
The SG0-5 has a rating of 546 sq.ft. of steam
I really cannot see how we are over sizing the unit.
This is why I ask, the customer relayed to us that the two other companies stated that the rating numbers by Weil-McLain already "bumped up" for pick-up loss.
Are we wrong??
  • icesailor
    icesailor Member Posts: 7,260
    Wrong:
    You are not wrong.
    Steamhead Member Posts: 18,211
    If the radiators
    measure 517 square feet by themselves, with nothing added to this figure, then the SGO-5 is the proper boiler.
    Consulting