fan coil units
keith_27
keith_27 Member Posts: 64
How would i figure btu or edr of fan coil units on a steamsystem. There are six coils with fans on one zone of this system. The other zone is 2" baseboard elements. This boiler is about 27 years old and has a small leak at a push joint when it first starts up in the am. It will have to be replaced in the spring.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,687
    Click on
    Conversion Factors at the top of the page.
    Retired and loving it.
  • keith_27
    fan coil units
    Thanks dan What forula should be used ???? The coils are all assorted sizes ??
  • DanHolohan
    It's
    Steam Fan Coil Loads (in pounds per hour) = CFM X Delta-T of air (in degrees F), divided by 800
  • keith_27
    fan coil units
    thank you dan