How should I connect two sections of steam cast iron baseboard at a 90 degree corner?

bruce_21
bruce_21 Member Posts: 246
I got some special fittings to go with the cast iron baseboard to connect two sections in a corner one for top tappings and on for bottom ones. They are flexy gizmos that look like they will reduce the size from 3/4 to maybe 1/2 inside. Will this cause a problem by making a dam and keeping condensate trapped in the first section of the baseboard unable to get to the return drain at the end of the second section?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • heatpro02920
    heatpro02920 Member Posts: 991
    Do you have a picture...

    I have a way to do it with no fancy fittings, but I want to make sure I am thinking of the correct situation...
  • bruce_21
    bruce_21 Member Posts: 246
    Sorry no pics

    Sorry I have no pictures. It's a 90 degree inside corner, The cast iron baseboard is tapped 3/4 top and bottom. I have trim covers for the corner but there isn't much space.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,634
    Bruce,

    is this two-pipe steam?
    Retired and loving it.
  • bruce_21
    bruce_21 Member Posts: 246
    It is one pipe

    This is a replacement situation. 16 feet of cast iron base board now fed by one pipe steam system. Supply is 1 and 1/2 inch steel almost flat run out from main line. This run out also supplies another small rad on the floor above. The existing base board has 3 cracks, 2 at the far end and another at a point just before the inside corner. Per Dan's book TLAOSH I plan to add a 3/4 or 1 inch (which is best?) return line from the far end of the baseboard back to the wet return. I'm wondering why this baseboard cracked in the first place. The two 8 foot pieces are joined together with 3/4 copper male adapters and 90's. How much will this baseboard expand? It is held by the exterior wall one one end and I can't see the pipe on the supply end because it comes horizontally out of a cabinet. Thanks for your help!
  • pipeking
    pipeking Member Posts: 252
    will

     a 3/4 blk union fit inside the trim? what about copper? 
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,634
    If it's anchored and expanding

    it can break. I think 3/4" should be fine for the drain. Don't forget the air vent.
    Retired and loving it.