#65 LWCO
I have a customer whose #65 is not shutting the boiler off in a low water situation.
Not real familiar at repairing them, ideas?
  • Macheat
    Macheat Member Posts: 2
    sorry MM #67 not 65
    my fault its a #67
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    edited February 2013
    A dangerous situation
    These can be taken apart, but if the interior float, and chamber are full of rust, you may want to replace the whole unit.
    A dry-fired boiler is a great fire, and safety risk.--NBC
    http://www.pexsupply.com/McDonnell-Miller?/
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    Manual
    Here's the manual and replacement parts list.
    This problem is what you see if the LWCO isn't blown down weekly. The rust and scale settle under the float so it doesn't drop when the water level falls.
  • ChrisJ
    ChrisJ Member Posts: 17,070
    Cleaning
    I took one apart and cleaned it, afterdwards it worked perfectly. I also showed the owner how to test it weekly with the burner running.