Steam trap
Chowdahead
Chowdahead Member Posts: 59
Help on this one please
  • RJ_4
    RJ_4 Member Posts: 484
    trap
    Looks like an old school F&T trap  with an external T part,  hard to say, describe   where the piping is coming from and going to
    Steamhead Member Posts: 18,508
    I think
    that's a "float trap/air eliminator" as described in chapter 15 of Lost Art. It is the only place where air is vented from the system.
    Is this device on the dry return near the boiler?
    Consulting
  • unclejohn
    unclejohn Member Posts: 1,833
    Looking at it
    Sideways I believe and my first thought was also some kind of vent.
  • Chowdahead
    Steam trap
    Yes the trap is located on the return
  • RJ_4
    trap
    Take a temp. reading from inlet to outlet, if the temp is the same this would indicate a problem with the trap, it can be replaced with a Hoffman F&T trap. there would be extensive repiping
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,712
    I agree.
    It's a central air eliminator. The float keeps the boiler water from flowing out the vent hole. It's not a steam trap.
    Retired and loving it.
  • RJ_4
    no trap
    Thanks Dan for the clarifiiation  looked like an old trap but the piping did not seem right
  • DanHolohan
    I'm glad you asked.
    A trap in that spot would have hurt.
  • Chowdahead
    Steam trap
    Thank you for the info, now for 64 thousand dollar question, what can replace it.
  • DanHolohan
    Is it broken?
    If so, a high-capacity main vent. But if it still vents I'd leave it.