Badly plugged sections
Paulien
Paulien Member Posts: 7
Hi Guys...Any advice to clean badly plugged up sections of a steam boiler?/ Tried the thin saw & brush on the sides but when I removed the jacket the top sections are cement like plugged in some areas..the little "nubs" are breaking off as I try to chip away..any liquid material to pour down to loosen up?  Thanks alot
  • billtwocase
    billtwocase Member Posts: 2,384
    possible
    leaking boiler if it has hardened the "soot" to the extent of calling it cement. I would seek a pro to determine that
  • RJ_4
    RJ_4 Member Posts: 484
    section
    I agree I would get someone familiar with your boiler to determine how to clean it   I would also get someone with a strong background in boilers who  can do a complete flue inspection ( proper flue size, fresh air,combustion air ) and a combustion analysis of the burner.     I would also put a co monitor in the boiler room.  Be carefull using any chemicals in boiler rm.  especially if there is other gas or  oil fired equip.in room.
  • icesailor
    icesailor Member Posts: 7,260
    Plugged Sections:
    Is it possible that this steam boiler has a hot water coil to supply domestic hot water and you are running the boiler as a "Cold Start" where the burner only runs when there is a call for heat or hot water? And the temperature controller is set low for domestic hot water use?
    I see what you describe in an account where there is ODR on hot water boilers and they usually run for most of the year at temperatures below 140 degrees. I clean them every summer when they are off with a soot saw and threaded rods with file handles. If I didn't clean them every year, they would plug solid with a grey cementious material.
  • kcopp
    kcopp Member Posts: 4,630
    if the pins are....
    breaking of... that's not good. You may very well have to put in a new boiler.... however I would find out what happened so you don't get a repeat
    Steamhead Member Posts: 18,209
    Try
    a long drill bit, no more than 1/4" diameter. Even if it doesn't get all the way in, it'll get some of that mess.
    The burner may be running with too much excess air, lowering the flame temperature.
    Consulting
  • Tony Massi
    Tony Massi Member Posts: 86
    Boiler Plugged
    You could loosen up the scale in the boiler by slowly letting some water into plugged flue sections. Just a very small amount, like just above a drip from a hose .You can use some water off the boiler drain with a short hose.Then try to open one section at a time, use soot sword and then a very small brush or a piece of ridged wire you will throwing it away when your done. Clean on an angle with the brush be patient. It may get a bit messy but its better than breaking off the pins on the boiler or getting a brush stuck in it or worse. If you do it right you will clean the boiler and get a proper draft over the fire. You will get some water into the chamber but it will burn out  I have done this a few times with success.
  • Tony Massi
    Boiler Plugged