adambuild
Member Posts: 422
I'm under the impression that you can run 2" exhaust and fresh air intake on the Prestige 110. I have a 24' horizontal run. Anyone done this? Any specifics I need to know?
0
Comments
-
2" venting
3" is better if you have the space. From http://www.triangletube.com/documents/1/Prestige%20Vent%20Suppl_PVC_CPVC_PP%20_SS_0412.pdf
2 Inch Vent Systems Restrictions for the PRESTIGE 60, 110 & Excellence.
- Derate the maximum boiler input by 3% when using the maximum equivalent length of 2 inch vent piping on Solo 110 & Excellence 110.
- The 2 inch vent system requires a 1 inch clearance to combustibles
- Use long sweep elbow to limit pressure drop and to avoid excessive vent temperatures.
- In 2 inch PVC vent applications, the first 7 equivalent feet of the vent system must utilize CPVC material.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements