have a company overing to sell me a steam boiler that is a 225K BTU to replace a 200K BTU existing. what are the consequences from using boilers not the correct size? thank you for your input.
We still didn't get an answer
from the last question we asked you, so I'll ask it again.
What is the EDR of the building the proposed boiler will be going into?0 -
EDR
If you don't already have the information to calculate EDR, this might help. EDR is the surface area of the radiators stated in sq ft. The first is from an old version of the ASHRAE Guidbook. The second is from Peerless Boiler and contains some VERY important information on the proper installation of steam boilers. The third is a simplified chart for calculating and adding up the total EDR of the system.Dave in Quad Cities, America
http://grandviewdavenport.com0 -
under + oversized steam boilers
i have just received holohans book the "lost art of steam" and waiting on the book from him also, EDR (Every Dam radiator). Reading at breakfast that it is indeed the radiation that is just as important or more so than the heat loss. plus a 1.5 factor on the DOE rating if i remember correctly.
i have an weil mcclain eg 55 located and the dunkirk wholesaler has a 225K BTU he wants to move out of inventory so figuring the 55 to be 200K BTU, wondering if 25K BTU will cause a proble? since the book was sent priority mail,,i should have it monday to see what the sq ft is in this big 2 story 1876 magnificient home built by a returning civl war officer in keokuk ia. it is listed on the national registration of homes. i have a new home + would trade for it since it has so much character.0 -
The problem is
that a lot of steam boilers that are now installed are just to big for the load they are driving. The edr of the house is all the boiler has to work with and if the boiler is to large it works but it's not very efficient. If the boiler is grossly oversized it won't work well at all.
Make a list of all the radiators (height, depth, number of sections and the number of columns per section). With that information you will be able to tell what kind of load you have to drive and thus what size boiler you need.
3PSI gauge0