Oil to NG Conversion
BostonGTR
BostonGTR Member Posts: 18
I’m converting from oil to NG.  13 yr old house with good insulation, windows and doors with 3 hydro-air units.  Given that the hydro-air units have aquastats set at 140 degrees; what is the best boiler solution?  Am I correct that a modcon unit will not be
in the “sweet spot” i.e. not condensing, due to the need to generate approximately 170 degree water for the air handlers; not to mention the need to generate hot water for an indirect DHW tank?  Even if the modcon is not condensing and therefore not operating at 96% efficiency; will it still be more efficient, or at least as efficient, as a new cast iron boiler?  I understand that the modcon would require some annual maintenance.  Is the cast iron boiler maintenance free?  The 96% modcon unit offers a rebate of $1,500; the rebate drops to $1,000 for a rating of 90%+; and then to $0 below 90%.  Might you be able to recommend a “medium efficient” cast iron boiler with a 90% rating?
  • SWEI
    SWEI Member Posts: 7,348
    rest of system
    Are other emitters (radiators, floor tubing, etc) involved, or just the hydro-air units?
  • BostonGTR
    Only Hydro-Air
    Just the 3 hydro-air units.
  • SWEI
    edited October 2012
    outdoor reset
    Works on air coils too.  The curve will be higher and steeper, but it will noticeably improve comfort and efficiency.  Depending on the coil sizing and the climate, a mod/con could be condensing more of the time than you'd expect.
    Edit: looks like the aquastat controls the fan, so making ODR work properly would require some additional controls.
  • BostonGTR
    Feedback
    Does anyone have any experience using a modcon boiler to feed a hydro-air system? It seems that it shouldn't perform any worse than a cast iron unit; correct?  I just want to make the correct boiler decision (modcon vs. cast iron) before proceeding with this heart transplant.