Secondary Loop Sizing.
jjheat
Member Posts: 35
I have 2 Alpine 399,000 btu boilers that are twinning in to a common secondary looop that needs to deliver 80 GPM. Is 2" large enough???
looking at Dan's
Golden Book of HH...2.1/2" would be better. 2" will only get you 50/45 gpm safely.0 -
Design range
Using the B&G "System Sizer Calculator" a 2 1/2 inch pipe is at the limit for "normally used design range" for 80 GPM. It has a friction rating of 4.5 Ft per 100 Ft of pipe, plus you must account for fittings and valves. This will affect your pump sizing.0 -
Alpine manual
The Alpine manual calls for a 2-1/2" common pipe where both boilers tie into the manifolds. The boiler piping (secondary pipe) is 2" per the manual even though the boiler tapping's are 1-1/2".0 -
If Each Boiler
Can only provide 37gpm output on a 20 delta, how do you expect to get 80gpm? Just curious. On a 20 degree delta 3" pipe will carry 77gpm or 770,000 btu/hr. Increase the boiler delta to 25, select the proper pumps per the manual and you can pipe the primary or boiler side in 2".There was an error rendering this rich post.