Oversized steam boiler - worth replacing?
elfie
elfie Member Posts: 266
what is rough cost to replace a 10 yr old cast iron steam boiler (14 section)?  the existing boiler has a capacity to produce 3 million btu's per hour.  the new steam boiler would be about 1 million btu's.
ideally, it would be better to install 2 smaller steam boilers each about 500 btuh each.
thanks
  • JStar
    JStar Member Posts: 2,752
    Well
    We do not discuss pricing in public. Where are you located?
  • elfie
    another way
    maybe another way to approach this dilemna is to ask it in another way.
    if you had a steam boiler with a capacity of 65 million btu's per day and you were only producing 10-15% of this amount on the coldest of winter days, does it make economic sense to replace boiler?  do people buy used cast iron boiler sections?
    the boiler probably has another 20+ yrs of life.  yes its costing a few thousand more per yr to run, but the payback is probably 15-20 yrs, which is too long.  So, I guess the only course is to endure more costly energy bills for the next 20 yrs.
    I suspect many are in a similar situation.
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,414
    The boiler may not have that much life left
    I am finding many over sized poorly piped commercial boilers that are failing after 6 or 7 years. How do you know the proper boiler size? Did you do a radiator survey of the building? On that size of boiler a staged burner with a vapourstat controlling it may be better to cut costs. What is the current boiler make and model? It may simply need a staged or modulating burner to give you big savings.
    cell # 413-841-6726
  • elfie
    burner control
    here is the burner pic (powerflame) for boiler (HB Smith) and related pressuretrol and cutin/cutoff devices (ie. controlling burner intensity and burner cutoff/cutin).  cutoff pressure is set at about 2.5 psi.  all the short cycling is unfortunate (purging is inefficient) and auto setting results in lower burner intensity but still short cycles.
    does all this represent a staged burner setup?
    is a boiler failure (shorter life) more likely due to severe overcapacity?
    also, have done a radiator sizing exercise and found that btu delivery capacity within space (one large room) being heating is one fifth of the boiler capacity (room is easily heated with existing rads)
    thanks
    can you take a photo
    from further back on your burner? It may be two stage but it needs to be properly tuned to save fuel when changing fire rate. also has the water seal been cleaned out for the pressuretrols?
    cell # 413-841-6726
  • elfie
    edited August 2012
    burner and pressuretrol settings
    better picture of burner
    i doubt the water seal on pressuretrols have ever been cleaned, what would this do? never heard about cleaning the water seal
    basically, all this boiler is doing is ultimately supplying steam to two 2 inch pipes that connect to blower heating coils - each blower is 3000 cfm (ie. a 3 million btuh boiler).
    thanks very much
    It would stop them from working
    I am refering to the 1/2" piping below the pressuretrols. Yes that is a two stage burner. It starts at a 50% down fire and can be down fired even further. Where is the boiler?
    cell # 413-841-6726
  • elfie
    edited August 2012
    boiler pics
    front and side view of boiler and the headers
    would down firing the burner resolve the excess capacity issue - how tough would it be to downfire the burner
    thanks
    for me or another trained burner guy it would be easy
    but easy is relative. Yes that is a reason the boiler is designed for staged firing. I have not walked in on a burner that was actually set to fire two stages even though a two stage boiler was paid for.
    cell # 413-841-6726
  • elfie
    two stage
    how would i know if its set for two stage functionality
    i am aware that the burner modulates, is this the same as two stage functionality?
    thanks
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    edited August 2012
    Modulation-the cure for oversize?
    Is this system your's, or a client's, or perhaps a possible purchased building? What maintainence has been performed on a regular basis? Has it been losing any water?
    My suggestion would be to have the burner(and boiler), serviced so as to make the modulation functional and see how it behaves. You can observe how it is working by watching the pressure on an accurate gauge. The fan-coil units may require a bit more pressure than regular radiators. A 0-4 psi vaporstat could be able to control the modulation of the burner, if you are lucky, but with the potentiometer, only a real expert like Charlie would know. Consulting the online documentation for the burner would tell you a lot about it's possibilities.--NBC
  • elfie
    edited August 2012
    steam coil pressure
    good point about higher pressure needed for steam coils.
    thanks
