Mod-Con Boiler Pump Speeds
Gave them to you
Look a few posts above. Don't be fooled by AFUE. Condensing boiler is only that efficient when you get return water temps down below 115 degrees. The most efficient condensing boiler is the one thst produces the most condensate...There was an error rendering this rich post.
I understand
This calculation does not take into account infiltration, convection, size of rooms . . .0 -
OK, I see them
It's just that you said 4.2 actually means 3.3 across hx, so I'm wondering if the other flow rates (5.5., 4.7), have lower rates across hx.0 -
Not What I Said
On speed 1 a UPS15-58FRc can only move 3.3gpm at 7' of head.. .That is where the HX curve intersects with the pump curve...There was an error rendering this rich post.
Got it
Thanks for the clarification. This stuff is complex . . .0 -
efficiency
The numbers you looking at are AFUE, annual fuel utilization efficiency , has nothing to do with boiler and system efficiency, and is a just a fanny number. What really affects efficiency are many factors, including proper installation, sizing, setup, return water temperature, load to installed radiation ratio and many more.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
infiltrations
infiltrations might add a lot to heat loss. depending on how tight is your house.Gennady Tsakh
Big difference between speeds 1 and 2
If pump speed 1 gives 3.3X(40X500) = 66,000 Btu and
pump speed 2 gives 4.7X(35X500) = 82,250 Btu
that's quite a jump - I guess it is a function of how those pump curves and hx curves intersect?0 -
Speed 1
Delta is going to be larger then 40 proabably 43 or so....There was an error rendering this rich post.
The house is as tight as I can make it
I'd say it is very good but not great. The roof cap is extensively air sealed and insulated. All the windows are good. The one big defect is that I can't get to the rim joist to seal it. My basement has a hard plaster ceiling with metal lathe. Getting to the rim joist would require some major destruction of the ceiling.0 -
We can get down into the single digits sometimes
but most winters the coldest days are in the low teens. Boston metro-west suburbs0 -
Bumble bee
That pump looks really cool. Now that you guys have educated me a bit, I can see the advantages of a true variable speed pump with temp sensors.0 -
Delta-T
It has always been my understanding, that the various delta-t options provided by mod/con manufacturers were provided to ensure minimum circulation through the boiler at various system delta-t's, and not that you could maintain a certain delta-t through the boiler.Some of the I&O manuals are not clear on this, and others clearly state it for selection of primary circulators.If you are shooting for this delta-t, based on system design, use this primary circulator.0 -
second guessing now
Just had someone tell me the flow on the secondary pump cannot be greater than the flow on the primary pump for a Viessmann 200. I'm planning my install and was intending on using a low loss header to decouple the primary and secondary circuits. I'm going to use baseboad radiators on the secondary side of the system (minimum 1 gpm per radiator), using a reverse return piping arrangement. I end up with approx. 12 gpm on the secondary side. Max primary is like 6 gpm per literature. Am I going to have any issues with my secondary circuit being a higher flow than the primary circuit?
From my understanding this was ideal but I just had a long conversation with someone whom says they deal with high efficiency boilers all the time and that my secondary loop cannot have a higher flow than my primary loop.0 -
There was a helpful discussion about this a few days ago on this wall
I am not a contractor, so I will let the pros answer your question.0 -
flows
The purpose of hydrolic separator is to separate boiler and system loops. So this discussion of flow differences is irrelevant in my opinion.Gennady Tsakh
Blind Leading the Blind
My friend Gennady is correct but I'll chime in.
When you use the LLH you have in essence two separate systems that have no influence over the other. The boiler will deliver the btu's and you will take them away. How the boiler delivers them is irrelevant to how you take them. In the case of Vitodens 200 we use a LLH sensor. It's purpose to is make sure the boiler is delivering the proper water temp to the LLH based on outdoor temp. In other words, the boiler is going to make sure the temp and btu's you need for that given time gets delivered no matter how yiu take them away.
If your friends theory was correct, ask him why Viessmann specs a pump for a 40 degree delta-t knowing most systems run at a 20 degree delta-t?
Bet you'll really get blown away to find there is no "TT" on the boiler to tell it there is a call for heat... Another subject for another post....There was an error rendering this rich post.
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 106 Geothermal
- 983 Plumbing
- 389 Solar