why are pumps calulated in Heads?
                
                    gurrieman69                
                
                    Member Posts: 3                
            
                        
            
                    i was in class and we went over pumps but the teacher did not have the answer and was hoping someone could help?                
                0                
            Comments
- 
            Pumping Heads:
What didn't he explain that you didn't understand?
I can give you a low knowledge comprehensive explanation but I need to know what you don't know or understand.0 - 
            heads
i know that it is a distance but why is it called head?0 - 
            lift
The convention of head as used in pumps comes from the amount of pressure required to lift water-as in an open system. At least the industry uses head for all pump measurements and does not use different terms. 2.31 feet equal 1 psi and one atmosphere is 34 feet.0 - 
            H.E.A.D
my teacher thought the reason we use "head" is because the letters stand for something. What?0 - 
            I don't know for sure
but since it always is expected to refer to a height, I imagine head is just referring to the fact that we're talking about the top of a column, or it's head.
If you have 15 ft of head available on the pump, it will push a column of water 15' high in the air.
I'm guessing, but I think it's a better guess than some mysterious acronym
                        Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0 
This discussion has been closed.
            Categories
- All Categories
 - 87.2K THE MAIN WALL
 - 3.2K A-C, Heat Pumps & Refrigeration
 - 59 Biomass
 - 427 Carbon Monoxide Awareness
 - 118 Chimneys & Flues
 - 2.1K Domestic Hot Water
 - 5.7K Gas Heating
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 3.7K Oil Heating
 - 73 Pipe Deterioration
 - 1K Plumbing
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
 - 3.4K Thermostats and Controls
 - 56 Water Quality
 - 51 Industry Classes
 - 49 Job Opportunities
 - 18 Recall Announcements