High Pressure Zone Valves?
MacPHJr
MacPHJr Member Posts: 66
Does anyone make a 3/4 c Zone Valve that will work in a high pressure hot water system. I'm having a problem with a typical Taco zone valve, bad water hammer as it closes which vibrates through the entire building.
  • Gary Jansen_4
    Gary Jansen_4 Member Posts: 77
    Taco Zone Sentry
    valves are a "ball" style of zone valve that may be what you are looking for. Go to taco-hvac.com for more info. Thanks, Gary
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,875
    edited February 2012
    Sounds to me like an oversized, out of control pump....
    Typical...
    Maybe you should consider either a pressure activated bypass, or a frequency drive based on delta P, and do your client a BIG favor.
    Remember, the solution is rarely in the same room as the problem.
    Another commonly overlooked fact, is that higher Cv valves have LESS resistance to blow by when closed (excluding cylinder and rotary ball type of operators).
    ME