Oil to gas sizing
Options
GJD
Member Posts: 1
i am replacing an oil boiler, rated for 1800 sq ft of steam. What would the gas replacement be in BTUs?
0
Comments
-
What is the EDR?
The math is to multiply the sq ft by 240 but before doing that do you have 1,800 sq ft of radiators attached?
You have to know how much EDR you have before you know what size boiler you need. to buy. A lot of old boilers are grossly over sized, if you want the new boiler to run efficiently do it right.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Ditto
Never assume that the old boiler was properly sized. Also the dead of winter is not the ideal time to replace a boiler. You want to be able be able to do proper homework. You also don't want the installer to be forced into doing a rush job.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements