Warren Webster trap?

Options
Are these still available? Or a replacement?

Comments

  • crash2009
    crash2009 Posts: 1,478
    Webster

    I have read other threads where others have recomended  http://www.tunstall-inc.com/?s=webster
  • gerry gill
    gerry gill Posts: 3,084
    out of business- sorry

    Like Crash said, use a tunstall or a barnes and jones repair kit.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Thank you

    Any tips on Identifying the trap ?



    I didn't see and other markings.  
  • Gordo
    Gordo Posts: 857
    I Hope for You

    that the numbers are on the body somewhere underneath all that paint.  It may be something like "533"



    Is that trap being used to drip a large steam main perhaps? 

    Hydrolevel VXT Fanboy

  • trap is on Radiator

    It is a bank building in center city Philly.  A train wreck ,,, the trap is on a radiator its a warren Webster system the boiler was sitting at 5psi when i got there the water was squirting out of the vents !  steel hammers were doing there thing.   Paint was thick. thanks again
  • Gordo
    Gordo Posts: 857
    The number should be on the trap body

    somewhere...usually on the side you can't get to.



    It may be a 7 series trap.



    Yeah, 5 psi is not enough...if they want to MOVE the building.  500 psi would do it.

    5 oz/in2 is all that's needed to HEAT that building.



    Were the squirting vents on the radiators perhaps?

    Hydrolevel VXT Fanboy