Jim Pompetti
Member Posts: 552
I'm looking at an old vapor system , The unit comes on , runs for 5 or so mintues , goes off briefly on low water .Water comes back to the boiler ,then for several minutes the air vent on the dry return, starts blowing air . Boiler starts and goes thru the the same scenario . Any thoughs??
0
Comments
-
vapor system
these old systems need low pressures-could the pressuretrol/vaporstat be allowing more than a few ounces of pressure, and what is the pressure? check the pigtail for blockage.
if the main vent is a hofmann 76[?], the restrictor plate under the cap may have stuck, and now no proper venting. try running the boiler briefly with the vent off [be careful, with your hand on the switch]. see if the water level does not drop. if replacement is needed, then replace other main vents at the same time with gorton #2's or multiples thereof.--nbc0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements