weil mclain wgo3
marsco
marsco Member Posts: 6
just installed with beckett genesis control, lights, then control chatters, then locks out. did not contact becett yet. any ideas
  • lchmb
    lchmb Member Posts: 2,997
    connections
    Is the control going to lockout? Or chattering and shutting off completely..no light's visible..
  • billtwocase
    billtwocase Member Posts: 2,384
    chatter
    Could be a defective control, but I would check all wiring, voltage input reading, secure all grounds including case grounding, etc. It most likely has a low water cut off aquastat. What lights are lit on top?
  • marsco
    Wgo3
    I'm going back today to check. it does have a aquastat with a low water cut off
  • marsco
    Solution?
    went back on job today, hooked up my contractors tool ,turned on power switch. no chattering. but 3 cycles showed pre time flame .I set up the burner and everything seems fine. Ran it threw a few cycles with the thermostats , it ran fine. Thanks for the input !
  • marsco
    Solution?
  • billtwocase
    I would
    Check your clean cut pump. The stem was stuck open? Is it programmed for pre-purge?
  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    Had some chattering
    after we accidentally spritzed a Genisys with water . Didn't want to take a chance so we just swapped it out .