Correct Water Level
Fellow steam-heads,
I've no idea what the water level should be on my old. I've added a 0-3PSI guage - would a safe assumption to fill the boiler until the new guage comes up to 0PSI? It is currently registering at less than 0.
Thanks,
Mark
    Steamhead Member Posts: 18,502
    The water level
    should be at 1/3-1/2 way up the sight glass when the boiler is cold. On most boilers it should never go below 1/4" above the nut at the bottom of the glass.
    If the gauge reads below zero, there may be a slight vacuum in the boiler.
    Consulting
  • Joe V_2
    Joe V_2 Member Posts: 233
    Why?
    Why half way or less?  I confess, I have been filling my boiler more than half-about 2/3's in the sight glass.
    I can't remember why I decided that this is the fill level. I might have chosen this level based on the slow rise and fall of the level when heating (about +/- 1/4 of an inch).   But more likely,  I chose this level because more than half is better than less than half full.  It is an IN-5.
  • ChrisJ
    ChrisJ Member Posts: 17,390
    edited October 2011
    NWL
    My Burnham V8 had its water line 3/4 of the way up the glass.  I found this by looking at the instructions and measuring with a tape measure.  A Burnham IN5 may follow the same rules
    The Weil-Mclain I am installing claims 1/2 way up the site glass.
  • Rod
    Rod Posts: 2,067
    edited October 2011
    WaterLine IN5
    The factory specified waterline is 28 5/8 inches above the floor level. Attached is a diagram from page 17 of the IN5 I&O manual.  On other boilers -The factory designed waterlines are generally  found in the steam piping sections of the individual boiler's I&O manual.
    - Rod
  • Joe V_2
    Yup!
    I looked it up when I got home and measured the NWL given by burnham and it was slightly higher than half way so I drained some water. I guess I'll get steam faster now. Glad I caught this thread.
  • Mark_125
    Mark_125 Member Posts: 56
    Old steamer
    OK, so I had a look at the boiler plate, its an American Standard G28, Model 7BNJ6.
    Anyone have any clue on where I might find the correct water level?
    Thanks,
    Mark
  • Joe V_2
    edited October 2011
    I think i might have had that exact model!!!
    I think you should trade it in for a younger model! you will save a boat load of cash.
    Each section must weigh five hundred pounds because even when I broke it down with a sledge hammer it was still really heavy.
    I ran that boiler at two thirds in sight glass too. Maybe that is where I got it- from the previous owner
  • crash2009
    crash2009 Member Posts: 1,478
    edited October 2011
    Beacon Boiler Reference Book
    I found it listed in the Beacon Boiler Book.  Page 12.  I don't know what numbers (if any) would tell you the correct height of the water line.  http://www.heatinghelp.com/files/articles/940/182.pdf  This should tell you the age though.
    Oh, I just noticed Steamhead all ready told you what is the correct level is 1/3 to 1/2
  • Mark_125
    Thanks Steamhead.....
    I guess I had it filled a little high. The previous owner had drawn a ring on the sight glass about 2/3s up.
    -Mark