After the fact kinking
NRT_Rob
Member Posts: 1,013
has anyone ever seen kinks show up in pex that was not there during an installation, but happened days afterwards? I've seen it and we're trying to figure out a cause. application is pex in heavy gauge joist plates.
Rob Brown
in beautiful Rockport Maine.
Kinking
What type of pex? What water temp? What spacing? Location of kinks?0 -
thanks for replying Greg
kinks at the loop bends, between 6" and 9" o.c. water has never touched the system... happened on 2 projects installed this year, one in the winter and one in the summer.
I would be very interested if anyone else has ever seen it. Personally I've never heard of kinks appearing AFTER an install.Rob Brown
Kinking
It it Pex A or B? Also. what diameter. Pex B is much less flexible. We have been using Rehau (pex A) for around 15 years, and I have never heard of anything like that.0 -
PEX A
I've never seen anything like it in 15 years either. I won't note the brand yet because we don't know if it's the pipe. but unless I can find some other examples of it happening to other brands....Rob Brown
Kinking
Pex doesnt kink itself. I suppose if there is too much stress placed on the tube on a return bend, there could be a reason to crimp. There has to be a common denominator. Spacing issue maybe? Could there be some kinking going on during install, that may be getting accidentally over looked?0 -
possibly
but having never seen this in 15 years I am having a hard time thinking that two different installers within six months of each other are making the same mistake. and I don't see any issue with the on centers.. the pipe should be able to handle what it's being asked to do in that respect.Rob Brown
Kinking
Same brand of pipe on the jobs?0 -
yes sir
and one installed in the winter, and one in the summer, so not even similar temperature conditions.Rob Brown
Kinking
Is it pex A or B0 -
it is
pexARob Brown
Kinking
I've never heard of self-kinking PEX before. This is a new one.
Have you contacted the manufacturer?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Straw grasping
Was the kinked portion of the tubing near the edge of the supply reel? My thought is that perhaps some sort of damage happened to the tubing while it was still on the factory reel.
Did both tubes come from the same shipment from the factory? What are the commonalities of the failures?
Same manufacturer?
Same lot?
Same wholesaler?
Same distributor?
Same type of location for the failure location?
Same people at both job sites? Not necessarily heating industry people, but someone else messing with the installation.
Any indications this was deliberate damage?0 -
Double post
were the bends.....
done opposite the radius coming off the reel?.... in other words if it had a Left hand bend to it was it torqued back to the Right hand... the radius is less then. Pex has the memory aspect.... it will eventually go back the way it was extruded. kpc0 -
good questions
same MFG, not sure of the lot. Same location for failure, no common people on either project and zero chance of deliberate damage.
I think it boils down to: if no one else has ever seen this before, it's gotta be the pipe. The installation method has been used (heavy plates in joist) for many thousands of installations out there... There are no other common factors.Rob Brown
oh yes
they are not seeing anything on their end.
Even if we broke the minimum bend radius, I've never seen pipe survive it only to kink later. that's the part that is spinning my noggin.Rob Brown
good question
I have no way of knowing that. but even then... wouldn't it kink immediately?Rob Brown
maybe...
maybe not. Uponor pex rings don't shrink back right away. Just a thought.0 -
well, by "immediately"
I mean in minutes, not weeks.
my theory so far has been that it survives the original install but then conforms and weakens... but I've never seen that occur in any pipe.Rob Brown
plates
you mentioned plates,
Heavy gauge or light, did the kink occur at the end point of the plate, or did it kink in in the middle of the bend?0 -
heavy plates
kinked halfway through loop head bend.Rob Brown
turns at plates
I'm sure you have photos, and respect that you may not want to share just yet.
Another theory , was the bend made some distance from plates say 6"-12" from plates,tubing, then start turn.
Even though you stated not active loop at time of kink, there must be some minimum expansion/contraction always occurring from ambient air fluctations. My guess tube may not be allowed to move at end of run. I think plate manufacturer's require 12" at end of joist?0 -
loops were free hanging
and it occurred at the "peak".
some loops exited the end of the plates and made a regular bend around
some pop out early and make the bend without shooting out of the end of the plate... the plates are tight enough to allow for that.
the plates are also tight enough that the only movement is in unenclosed pipe... so just the bend itself, in these cases. pipe in the plates doesn't move.Rob Brown
are the bends
really close to where the tube comes out of the plates. I've kinked tube when the loop ends are pulled too close, but it happened during the installation.
How do you know when they kinked? Pictures of the original installation?
hrtBob "hot rod" Rohr
not really
kinks are at the "Peak" of the loop bend... equidistant from the two plates. right where you would expect a kink if you bent it too tightly but we shouldn't be too tight.
I have 2 installers giving the same story though, no kink during install, checked it out later and there was a kink. So I think the report is reliable.Rob Brown
I don't think it was an install issue
Although you could slightly kink it without immediately noticing, especially when your pulling the long loops into the bays. How about the moisture content of the wood you're attaching the plates to? Was it new construction, or in the case of the summer install, lots of moisture that was in the wood without the benefit of the AC running? Otherwise, I'm just as perplexed. Like you said, you do it the same way a gazillion times, then this.There was an error rendering this rich post.
Kinking
I think that the tubing was stressed at the apex of the bend. The likelyhood of pex "a" to kink by itself is extremely low. My bet would be kinking on install.0