ph level in steam and h20 boilers
hi
 in Dan's we got steam book he talks about the ph level in boilers i have never ever tested the ph level in a boiler so i bought some test strips and tested my residential boiler . and it was 6.8  which i think is alkaline
 what should the actual ph level be in a steam or  h2o residential  system?
 also Dan talks about adding vineger on page 46 of his  book
 . but how much vineger do u add? i by  the btu rating of the boiler? of the gallonage of the system
  thank you  bo ramsour , lakewood , colo
  • Jean-David Beyer
    pH
    Actually, pH 6.8 is very slightly acidic. But pH paper is not all that accurate.
    Technically, pH 7 is neutral. Less than that is acidic, and greater than that is basic.
  • Rod
    Rod Posts: 2,067
    edited July 2011
    PH in Steam Boilers
    Hi - As JDB said  7 is considered neutral. (I've attached a PH scale/explanation below - Note the numbers are logarithmic)  Generally for steel /iron boilers (not aluminum!) the more alkaline the water is the less chance of corrosion. In Dan's book ,"The Lost Art of Steam Heating" P 281- 282, he mentions that "Weil McLain recommends you keep the PH in their boilers between 7.5 and 8.5". You can use sodium hydroxide (caustic soda) to increase PH.  Rhomar Water  http://www.rhomarwater.com/products/residential-steam-system/   has some good products that will do this and also protect your boiler.
    - Rod