Erie 2 way zone valves
Steve_210
Member Posts: 647
Having some noise problems with Erie 2 way zone valves. Pretty sure it is velocity noise. When I remove the head (actuator) noise stops completely, but when you put back the head the noise starts again.
Also could anyone tell me what 2 port zone valve has the highest CV value.
Any advise greatly appreciated.
white rodgers
do one with cv of 23.5.
We normally use honeywell. has anyone had a good track record with W R or other other manufactures.0 -
Removal of the operator
should not impact noise or flow. Is it a Pop-Top style?
After many trials and failures, I've settled on Danfoss as my favorite zone valve since we've had no failures or issues.
Cv's are lower, but they've never been a problem.
http://na.heating.danfoss.com/PCMPDF/Zone%20Valves_Brochure.pdf8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
thanks alan
i spoke to Erie, They said that because it is a paddle type zone valve, removing the operater allows the paddle to open more thus reducing the velocity noise
I am looking for a zone valve with a high CV but am cautious about using a
new brand, what do others Like?0 -
Why?
Just curious: why do you need such a high Cv? Is it common to flow more than 2-3 gpm per zone?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
it is
an apartment building, I have no control over the boiler room. differential by pass may be another option.0 -
Bump
Any coments0 -
Knowing the flow rate
would be a big plus in selecting a valve. A pressure activated bypass or a delta p circulator are a few other fixes.
Th higher the Cv the less shut off pressure of the valve, generally. So a larger orfice valve may solve one problem but create another depending on the delta p that circulator creates.
Pull the spec sheet on various valves to see the difference. Look at close off pressure, operating temperature, type of construction, etc to find the best valve for your application.
Here is a spec sheet on two different brands to compare features.
If you do suspect excessive flow, address that. The valve you have will work fine if you install a PAB or smart pump.
hrBob "hot rod" Rohr
Living the hydronic dream0