Trap Application
Ed_68
Ed_68 Member Posts: 3
A multiple riser building I am working on has a thermostatic trap at the base of each riser. There are over 15 risers on each of two zones. The system is a vacuum system and is consistently maintaining 8". System pressure is 5# at the boiler header. Should I be considering F&T traps at these locations?
  • gerry gill
    gerry gill Member Posts: 3,083
    not really,
    if the system was designed with thermostatic traps and they have been working for years its probably more economical to stay that way.
    gwgillplumbingandheating.com
  • five pound vapor system
    if the system is getting up to 5 psi, then that is why the traps are not working, as it is out of their range. get a 16 ounce vaporstat to be sure the pressure is in the range of ounces. also check that the air is escaping with a back-pressure of 2 ounces, using a good low pressure gauge [gaugestore.com, 0-15 oz.].--nbc