Summer winter hookup / indirect water heater / conventional electric hot water heater

Hey, I have a burnham RSA110 oil boiler with a summer winter hookup, and I wanted to attach a electric hot water heater to it. The plan is put a circulator pump on it and have the potable water pass through the existing coil of the summer winter hookup built into the boiler. Indirect water heater tanks seem pricey and I don't understand why I would need to have a tank with another coil in it to heat the potable water. I would love to turn this boiler off out of season and just use the electric to cut heating costs.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • billtwocase
    billtwocase Member Posts: 2,384
    what is

    a summer/winter hook up? If the boiler will be shut off, I would suggest not piping the electric tank thru the coil.  I would also have it serviced just before it is shut down for the summer so come fall it won't be plugged. I would look into a better boiler if savings are what you are after. This is a dry base steel boiler that is not a very efficient or long lasting. JMHO
  • jimmieskips
    jimmieskips Member Posts: 3
    burnham rsa110

    Hey Bill thanks for the quick reply. This boiler is about 4 years old and came with the house when I bought it. In terms of oil heat I looked around and the raiting on this boiler is I think 82.5% aflu, the most efficient oil boilers are 86% aflu. I am not super familiar with boilers just what I come accross online. From what I have read on here I do plan on putting a temar 423 Controller on this unit hopping the outdoor reset and indoor sensor do help a bit on the economy of this thing.
  • billtwocase
    billtwocase Member Posts: 2,384
    a good start

    and separating the hot water will save you some oil. It will last you a few more years, but have the chamber checked on it yearly with the annual servicing. They do fail on these.
  • jimmieskips
    jimmieskips Member Posts: 3
    A summer winter hook up...

    A summer winter hookup runs all year round to provide hot water to the house.
  • Steamhead
    Steamhead Member Posts: 17,699
    edited February 2011
    There's a difference

    between a summer-winter hookup with a coil, and one that uses a tank of some sort.



    The coil has a limited heat-transfer surface, so the boiler must stay at 180 degrees all the time to satisfy any hot water demand that may come. This is not very efficient.



    With a tank, the boiler only fires when the tank or the heating system calls for heat. So the boiler does not have to stay hot 24/7/365.



    One type of tank is a "booster", which uses the boiler's coil to provide the heat. This will store hot-water but may take a while to recover because of the coil's limited heat-transfer surface.



    An indirect tank has its own heat exchanger, which is more extensive than that of a coil. So it will recover more quickly and produce more hot water at less cost.



    With a well-insulated tank, the boiler may only have to fire once a day to maintain temperature if no hot water is being used.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting