heat for master bath
mwalsh3
mwalsh3 Member Posts: 7
I just finished renovating my master bath (live outside Boston) which is about 6' x 10' in size. I currently do not have any heat in the room (small oversight!), but it's actually pretty comfortable as long as I leave the door to the bedroom open. My wife doesn't share this opinion, however, so I'm trying to figure out the best option to add some heat. I have a 10 yr old FHW system in the house with the loop from the old bath capped off in the basement (which is completely open). Reinstallling a baseboard isn't a great option as I don't have a lot of open wall space with the new design the baseboard Some options that I've considered:
1) electric wall heater which is easy to install, low initial cost but might get expensive to run through a cold winter?
2) runtal towel warmer. Could use electric (which I can install) or hydronic (need to get a plumber), doubles as a towel warmer but cost is high
3) install radiant floor heat in the joist bays. My bath floor is tile over 1/2" CBU over 1/2" plywood over 3/4" planks and I have easy access from my basement. I don't know much about this option (can I connect to the old FHW llop, cost of install)?
Any thoughts or suggestions?
Thanks,
Mike
  • Brad White
    Brad White Member Posts: 2,399
    edited January 2011
    Door Number Three
    Depending on your heat loss, in fact, I will come right out and say it, you are not likely to heat your entire bathroom by radiant floor alone. But given the easy access, I would do it just because you can!
    The factors that are working against you are the relatively high resistance between tubing and tile, about R-2. The other drag on this is the useful area available. Even if you "radiate" the entire floor footprint, what is under the tub and vanity will not be as useful to you as open floor.
    What is working for you is the easy access. In fact, a hydronic towel warmer combined with the radiant may do it, if calculations support it.  If you can do the radiant floor, installing a towel warmer is easily within reach. Warm floors and warm towels are a wonderful thing. The other thing that is working for you is that leaving the door open between uses helps a lot. It also says that your heat loss is not insurmountable. Regardless, it has to be calculated.  But if you go that route, use extruded aluminum plates and insulate well underneath the floor once you are done.
    As for cost of installation, we do not discuss pricing here.
    I am not an installer, (except for myself),  but do live outside Boston myself, Newton by the way.
    My $0.02
    Brad
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"
    -Ernie White, my Dad
  • mwalsh3
    calculations
    thanks for the quick reply.
    How do I go about calculating if the radiant (and maybe towel warmer) will be enough for this room?
    Steamhead Member Posts: 17,892
    You would have to use
    a heat-loss calculation program geared toward radiant. I think Watts Radiant might have a free version of this.
    Also consider operating cost. Electric heat has the highest cost per BTU in most parts of the country, unless you live in an area with a lot of hydro such as TVA or the Pacific Northwest. This will drastically increase your utility bills.
    Consulting
    hot_rod Member Posts: 25,344
    Have it both ways
    I have in slab radiant in the bathroom. Nothing beats a warm, dry bathroom floor. I added a Runtal electric towel bar also. I use that in the shoulder seasons, as the heat, before the wood or LP boiler are fired up.
    I have it on a timer and thermostat so it can start up an hour before we get up, and for showers in the evening. You can fine tune the output by adjusting the amount of "towel" you put onboard. It warms much more quickly then waiting for the floor "'flywheel" to rev up and belch warmth.
    hr
  • If money grew on trees.......
    I would heat the floor using PEX tubing and aluminum plates AND have a Runtal hydronic towel warmer.  The floor heat would somehow have a floor sensor to keep the tile warm even when the air temperature has been satisfied.  And like Brad said, the heat will have a hard time getting through the flooring to the tile, so the floor sensor is essential.
    Since there's only one room, I'd be happy to calculate the heatloss.  I need the following information:
    - design temperature for your area, i.e. the coldest average temperature
    - dimensions of the room (6' x 10')
    - height
    - square feet of windows and outside doors
    - single or double glazed windows
    - linear feet of exposed wall
    - how many exposed walls
    - how much insulation in the walls, ceiling and floor
  • Brad White
    Mike- you can
    contact me off-line if you like. For one room, I can calculate that as a courtesy, no problem! Can also create a layout if you like, given you are in my area.
  • Heatloss
    Maybe let Brad and I calc. the heatloss independently and see what numbers we come up with.  Others could join in as well and we could compare numbers and heatloss software.
  • Brad White
    THAT, Alan, is a fantastic
    idea. In a number of ways.
    Good suggestion!
  • Paul Pollets
    Paul Pollets Member Posts: 3,669
    Electric Mat??
    I'd use an electric mat, if the tiles aren't installed yet.
  • mwalsh3
    calculations
    thank for the offers to do the calculations - here's the info:
    ** I live just north of Boston, and would guess average winter temps are in the 10-20 deg range. We just had one of the coldest days in recent history (-5 for a low) so that's probably a worst case
    ** more accurate dimension is 5'10" x 9'3", which includes a 5'10" x 2'8" shower
    - height
    ** 7'7"
    ** one window (5.5 sq ft) and 1 interior door (~16 sq ft)
    ** double glazed
    ** one exterior exposed wall 5'10"
    ** one
    ** R15 in all walls, about 12" of blown in stuff in the attic, nothing in the floor
    Thanks again.
  • Brad White
    Weather Data and other questions
    Being a Boston-based person, I can take the lead on the technical issues, if that is OK.
    The ASHRAE winter design temperature for Boston (granted this is at the airport, surrounded by water), is 9 degrees. Outlying areas, but inside Route 128, we would use 6 degrees.
    FYI, if you are talking "average", most people are surprised, but Boston winter average is in the  high 30's, 38-39 degrees actually. It is the cold snaps we remember. But the "design" temperature occurs less than half of one percent of the time and this is the number we use, accepting that the record for Boston was -18, recorded during The Great Dog-Hydrant Unity Parade of 1934. Median for January is about 29.5 degrees, half higher, half lower, so you can see the spread. But design, I would say 6 degrees.
    Mike, if you can be more specific, we can pin that down further. Not a huge issue in the scheme of things.
    Understanding that there is no insulation in the floor, what is the temperature in the basement below? Is it at least indoor basement space?
    The R15 in the walls, I will presume 2x4 construction, probably a lot of framing percentage given a window in a short wall, and high density batts. Sound good?
    I trust that there is a bathroom exhaust fan. Does this duct directly outside? That can be a disproportionate air leak for a small room, even with a flap damper. But let us know.
    Otherwise, enough for me to get started. You other guys?
    Brad
  • mwalsh3
    calculations
    Brad,
    I live in Swampscott, which is just north of the airport - I'm about 3 blocks mile from the ocean. Does that help with the temperature question?
    The basement below is indoor space (my workshop) which is ~67 degrees.
    The window is new and my contractor beefed up the framing in the installation, so that wall is high in farming percentage and I used the high density batts.
    The fan is a Panasonic that vents outside - dampers in the fan itsels as well as outside on the vent
  • Brad White
    Good to go, Mike
    That helps. I will still use 6 degrees. How windy is your location?
  • Nick W
    Nick W Member Posts: 200
    Heat lamps in the ceiling work well.
    We have a weirdly shaped bathroom that is hard to heat. It has 4-1/2 feet of baseboard radiator, but the radiator is poorly located to heat the entire bathroom. The builder wisely installed two 250-watt heat lamps in the ceiling. These add about 20 Btus/sf and make the bathroom very comfortable for bathing. The heat lamps are operated manually with wall switches. They warm up the floor very quickly.
  • mwalsh3
    calculations
    wind is not bad at this location
  • Brad White
    First Pass
    My first pass has your room heat loss at about 900 BTUH. The variables or rather, where your measurements are not taken precisely, is that you have the net inside dimensions of the space and not the outside edges of the volume. Specifically, your 7'-7" ceiling height does not define the wall height. I would assume 8 feet for those because one has to consider that the "wall between the floors" also has heat loss. Likewise your width and actual conducting area is wider than our net room width. Does that make sense?
    Anyway, my first pass is my newer program, LoopCAD 2010, which has a nice little BIM engine to generate 3D views. I took a guess at your joist spacing and orientation. I will follow up later with another method.
  • Heatloss
    My numbers come out way higher than Brad's.  I'm using Slant/Fin's Hydronic Explorer and the heatloss at the design temperature of 6 degrees outside temperature is 1,535 BTU's.
    Maybe we need to compare factors:
    doors and glass - .65
    exposed wall - .07
    ceiling - .02
    floor - .15
    infiltration - .012
    Brad calc's. 15 BTU's per square foot and I calc. 26 BTU's per square foot.
  • Brad White
    That was one of my
    first times using the LoopCAD program and I will do it both manually and with CHVAC to check it out, but I too was surprised it was that low. It is just one wall and window, good roof. Infiltration is the big dog and that may not be much. I lean towards your numbers though as a gut check.
  • Brad White
    Numbers In
    I calculated this by hand and using CHVAC and came up with the same numbers within 5%.  Indoor temp. at 72, outdoor temp. at +6. Delta T = 66F
    Rounded, 1,000 BTUH which benchmarks out at 20 per SF. Range 992 to 1018 BTUH.
    Factors:
    Net Wall: u= 0.071
    Glass: u=0.68
    Roof: u=0.033
    Floor: u=0.05 (but at a 10 degree DT)
    Infiltration: Crack method at 0.5 cfm per LF, face exposure method, ACH method (0.75 ACH) and volume method, all came to a range of 288 Btuh to 384 Btuh. I used 375 as an average of the methods, favoring the higher.
    Depending on the net radiant area, radiant floors might do the entire load, but I would put in a towel warmer just the same. Loss of radiant floor by the vanity, water closet "hold back" area and such, would favor that.
    So, radiant with a floor sensor, small mixing valve and small circulator should be plenty. Roth Mini-Shunt maybe?
  • mwalsh3
    calculations
    thanks for your efforts.
    Just want to make sure that when we're talking about "radiant" in this case it's the type that can be installed under the subfloor - in my case in the joist bays in my basement as my tile is already installed?
    Sorry if I wasn't clear on this from the start
  • Brad White
    Clear to me...
    Yes, underfloor with extruded plates, barrier PEX tubing. With radiant, your "back load", the higher BTU loss downward even with insulation, is a decent portion of your hot water heating load because of the higher temperature difference. Even so, your total flow rate will be less than 0.20 gpm. The smallest pump you can find may have you wanting to put radiant floors in the mudroom, doghouse...
    Which way to your joists run, parallel or perpendicular to the length of the room? And the spacing, standard 16" OC?
  • mwalsh3
    questions
    the joists run parallel to the long dimension of the room. If this does require addition of a new zone to my boiler (?) would it be possible to extend the radiant to the master bedroom? For some reason this is the coldest room in the house.
  • Brad White
    For the effort
    and assuming that the underside of the bedroom is similarly exposed below, I would do that too.
    Here are the basic rules:
    Heat loss needed for each space. If the floor coverings are similar (I doubt you have tile in the bedroom but the overall R value is the same), you can use the same temperature water to each, so one zone to do both.
    Regardless of what else you do, yes, you will create another zone, defined by a circulator, mixing valve and controls, to make a reduced temperature water circuit for your floors. If your bedroom has appreciably different characteristics, it MAY require a different water temperature. If we play our cards right, we may be able to get them both to have the same temperature. If the bedroom already has some heating source as it should, then the radiant becomes less critical and we can use it to take the edge off.
    But yes, all things are possible and it will justify the base expense of the circulator, manifold and controls. Beyond that it is piping, plates and insulation.
  • icesailor
    icesailor Member Posts: 7,260
    Existing Heat:
    Waz-up? You have 4.5' of existing baseboard? That works out to be 2200 to 2700 BTU's. More than twice what is needed and calculated. Over the years, I find that a bathroom this size is 900 to 1000 BTU's with 20% added for extra in bathrooms. I always install 3' of Slant/Fin rather than cut it. If it was 1500, I would have gone with 4' rather than risk a cold bathroom if they run the fan in the winter.
    If this bathroom doesn't heat properly with 4.5' of baseboard, something is wrong. Those infra-red ceiling lights are piercing the insulation and the heat is being sucked out of the bathroom. For me, personally, there isn't a way on Gods green earth I would put radiant in the floor of a bathroom as small as this without putting a K42 or a "Quiet One" kick space heater to heat this place.
    But hey, that may work for you. I've not seen it work for anyone else but it might work for you.
    750+ BTU's for the floor? That's a foot of baseboard. If the floor is insulated over a warm space, it should be more like 150+ BTU's.
    JMO,
  • Brad White
    The bathroom now
    has no heat at all, an oversight.
    Good points on the heat lamp disturbing the insulation.
    BTW, with radiant, given the insulation below and that it is a "positive", the heat loss is not to the room but to the system. A minor point, I admit.
  • icesailor
    Radiant Floor
    Only if the system water is colder than the floor. Heat flows to cold, dampness flows to dryness. If the water in the radiant loop is hotter than the floor, the heat is flowing into the floor.
    As I understand it.
  • Brad White
    As far as
    room heat loss is concerned, a radiant floor, especially being insulated as it should be, and especially if operating, has no significant heat loss, especially being above a heated or semi-heated space. Point being, when radiant floors are used, the heat loss is a negative number (negative from the total being positive to the space).
    However the "load" is factored into the radiant flow and temperature calculation, just is not factored into the room heat loss.
  • OneHungLow
    OneHungLow Member Posts: 11
    Roth mini shunt
    Hi Brad and all, You mention the Roth Mini Shunt....a nice little ****'y, but limited to 122 degrees. Are there other manufacturers pump packages like this that are comparable with a high temp, 180 degree, zone? The product availability is dizzying for those of us on the low end of the learning curve.
  • Brad White
    122F limit on Roth Mini Shunt?
    I did not know that!
    If so, what a shame, that nice entry level product.  I learn something new every day.
    And for that, today you will be known as "Other One High!" :)