I assisted today at catholic school in Brooklyn ...
jpf321
jpf321 Member Posts: 1,568
retired catholic school in brooklyn being repurposed as artist space ...
BACKGROUND
+ 2 boilers .. 14section HB Smiths (Mills 450) .. each rated for 9,225sq ft of steam .. <a href="http://www.smithboiler.com/html/mills4500A.asp">http://www.smithboiler.com/html/mills4500A.asp</a>
+ Carlin 1050 #2 Oil burners .. underfired ~7gph .. hi/lo/hi inoperable (only hi likely due to underfire and 0-15psi pressuretrol setup)
+ 1-pipe steam .. 36 classrooms + Modines in the basement .. not sure of total EDR .. corner classrooms with 4 rads, others classrooms with 2 rads + stairways, halls and bathrooms.
+ 141pieces of  2-column true-steam rads
+ main venting/system venting .. lacking severely ..
+ fuhgedahbout any kind of system balancing ..
The previous knuckleheads had stuck a condensate pump on the end of return .... with sarco traps and strainers prior to pump .. guess what .. pump kept returns dry .. and it was jackhammer city in the basement. End of 2 mains joined above water line (well the returns were dry, everything was above waterline) causing short-circuit of steam.
1 major leak in under-floor/buried in soil pipe and minor leak in 3" return line coupling. boiler would be overfilled each day and lose it's full load within 5hrs of steaming.
some radiators in school stone cold .. first priority of the Parish is to heat all rads.
Proposal for work (originally penned by me)...<span style="color:#FF0000">PREVIOUS NOTES IN RED</span>, <span style="color:#7777FF">CURRENT IN BLUE</span>
The outline of work to be performed is as follows:
    Pastor's/System Goals:
        1) provide heat to all upstairs radiators in a timely and efficient fashion
        2) fix leaks to eliminate loss of system water
        3) attain high/lo/high firing to decrease fuel consumption
    Methods:
        To address full system heating:
    1) Cut out boiler room return traps/strainers, abandon return pump,
join return pipes in boiler room, return water through pipe on floor of
boiler room <span style="color:#FF0000">DONE</span>
        2) Install "False Water Line"/Gifford Loop to
fill returns above raised return section in far music studio and "joined
returns" at end of mains <span style="color:#FF0000">DONE..FALSE WATER LINE SET AT 71" FROM FLOOR..THIS HEIGHT PROPERLY FILLS FAR MAIN CROSSOVER CONNECTION.</span>
        To address timely/efficient steam delivery to system radiators:
    1) Install capacious venting at end of mains and/or other vent
points in basement using adequately sized Gorton #2s vent trees <span style="color:#7777FF">DONE 16 pieces in total in various locations throughout basement</span>
    2) Drill and tap and vent risers on 4th floor if possible/accessible
to deliver steam quickly to the risers. 4th Flr Riser Venting to be
installed would be Gorton Ds or Gorton 1s unless it is
determined/feasible to install Gorton #2s. <span style="color:#7777FF">DONE .. only in back of school that was NOT getting any heat</span>
        3) Double check and ensure that all abandoned zone valves are as completely open as possible. <span style="color:#7777FF">DONE</span>
        **** Radiator venting maintenance and Radiator Supply Valve maintenance would be the responsibility of school staff. ****
        To address leaks:
        1) Fix leaking coupling in area of stacked desks (boiler room side) **** school staff responsibilty to clear desks <span style="color:#7777FF">DONE .. it had a sand hole</span>
        2) Fix leaking flange-union in area of stacked desks (end of mains side) **** school staff responsibilty to clear desks <span style="color:#7777FF">DONE</span>
    3) Fix leaking pipes/fittings on semi-buried return outside boiler
room consider removal of soil from around the pipes to eliminate
accelerated future leaking. Use some kind of lining or blocking as/if
appropriate to eliminate contact of pipes with soil/concrete. <span style="color:#FF0000">LEAK FIXED, CONCRETE LINING ON MONDAY</span>
        4) Fix leaking valve/vent above music studio control room door near end-of mains. <span style="color:#7777FF">DONE</span>
        To address hi/low/hi in order to decrease fuel consumption:
    1) Install new nozzles to deliver proper amount of fuel to the
boiler .. currently 4 hi/4 hi /9.5 (low) (17.5gph) proposed 4.5 hi/4.5
hi/12 (low) (21gph) .. all current nozzles are SS-45deg <span style="color:#FF0000">NOZZLES PURCHASED 7H/7H/9.5L</span> .. <span style="color:#7777FF">DIFFERENT NOZZLES TO BE PURCHASED .. 7/7/9.5 would not get clean</span>
        2) Retune combustion settings as necessary ..
        3) Adjust pressure controls/install vaporstats to allow switching from low fire to high fire based on system pressure. <span style="color:#FF0000">VAPORSTATS INSTALLED AND ROUGHLY ADJUSTED</span> .. <span style="color:#7777FF">ONGOING .. may need 0-16oz for LHL rather than the currently installed 0-4psi</span>
        4) Mark proper boiler waterline for proper water fill maintenance on sight-glass. <span style="color:#FF0000">WATERLINE
TO BE HELD AT 69" FROM FLOOR USING MANUAL RESET AUTOFEED (MM 247-2) (AUTOFEED ON
MONDAY)...WATER USE METER TO BE INSTALLED TO TRACK FRESH WATER INFLOW .. <span style="color:#00FF00"><span style="color:#7777FF">DONE .. Istec 1701 meter installed. </span>
<span style="color:#7777FF">NEW ITEM: Install Garber Spin on Oil filter (11BV-MK) as an additional secondary filter. </span>
</span></span>
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
    Steamhead Member Posts: 18,205
    Let us know
    how well it works!
    Consulting
  • jpf321
    oh yeah .. forget daily status update...
    Today we made significant progress. We eliminated the
    pump, installed the false water line, installed new 0-4psi vaporstats to
    replace old 0-15psi pressuretrols and fixed the leak in buried line. The
    buried leak was significant and required digging up and
    replacing the underfloor pipe from the exterior wall to the oil
    tank wall. They will line the bottom of the trenches with cement.
    On Monday, they will install the auto waterfeed (MM 247-2) and water use
    meter. And fix the leak on the 3" line.
    Perhaps on Monday, but likely another day, the
    boiler firing will be corrected and set the pressure controls for Hi/Lo/Hi firing.
    Also on another day (since the G#2 order is only being delivered on
    Wednesday next week) the venting will be addressed on the mains
    and the top of the risers.
    Upon leaving today, there was no knocking whatsoever due to the
    returns now being properly filled with water rather than empty.
    Unfortunately, the cold rads in the restrooms and some classrooms were still stone cold. We feel that proper boiler firing and system
    venting will correct these rads.
  • jpf321
    edited January 2011
    school update ...
    + all significant leaks have been fixed
    + MM 247-2 manual reset LWCO/auto-feed installed at proper water-line height.
    + Istec 1701 water meter installed on feedline.
    + 16 Gorton #2s installed throughout various points in basement .. one at bottom of each riser, end of mains, etc.
    + top-floor-minus-1 risers drilled, tapped & vented
    + overhead boiler room zone valves (operationally abandoned) fully opened by hand
    today was the first days in probably YEARS that the system was silent and that heat was delivered to rads that haven't seen heat in years.
    Unfortunately, the work isn't quite complete since the boiler firing needs to be tune in. Being that today was sunday, the necessary nozzles for final adjustments weren't available since the houses were closed. the nozzles which were originally  purchased (2pcs of 7gph), couldn't provide a clean fire. As well, the 9.5gph low fire nozzle wouldn't hold the steam. The original firing rate of 17.5-High does not make enough steam to heat both the front and back of the school .. the 23gph it was fired at today couldn't get cleaned up (but provided enough steam for the entire school) .. the thought is to shoot for around 20/21gphHigh and bring the Low up to around 11/12.
    I have updated the TOP post with the original scope of work in BLUE ABOVE
    I will report as this is completed.
  • Steve_175
    Steve_175 Member Posts: 242
    Pics?
    How about some pics of the work? Include one of the outside of the building.
  • Dave in QCA
    Dave in QCA Member Posts: 1,806
    Fantastic!!
    JP, fantastic project, and sounds like you hit every issue precisely!  I thought you were just a homeowner of a steam system.  Is steam work a new venture for you?  I am interested in this subject, as I see a very large amount of bad work here in the Quad Cities.
    Dave in Quad Cities, America
    http://grandviewdavenport.com
  • jpf321
    edited January 2011
    pics and you shall receive....
    Here are the pics, nothing really earth shattering ..
    http://picasaweb.google.com/jpf321/StCSSchool?authkey=Gv1sRgCJv7mq3EuMPKcw#
    Sorry No pics of below items...
    3" returns most everywhere.
    9" headers from each boiler.
    everyone's seen pics of G#2s so I left them out.
    operational modines throughout basement.
  • jpf321
    edited January 2011
    got bit by the bug hard ...
    my wife too thought I was just a happy homeowner .. until she started losing me to boiler rooms of friends and family .. the Pastor of this Parish school was my 2nd Grade Phys Ed instructor and he presided at my sister's wedding this past summer .. of course we got to talking bout steam over dinner ..
    fortunately, i'm a bit of an apprentice/assistant/gopher with one of the best commercial steam men/heating mechanics in NYC. i have the pleasure of being closely involved in the work when I stumble upon an interesting project, often because I am usually the main personal contact (sister's building, this school, the bronx brothers, etc.) and the friends and family expects me to walk the walk since I talk the talk.
    i am privileged to have access to all the right introductions, and meet all the various supply house guys .. (they seem to take you more seriously when you are hunting around for a 12gph Hago nozzle or picking up an order for 20pcs of G#2 and walk in with a Brooklyn Diocese Tax Exempt form.)
    i have learned so much..and although my wife misses me, i love the involvement and the experience.