Hydronic Heating with Tekmar Control - Intermittent Problems
rsuleman
Member Posts: 3
We have hydronic heating system and Tekmar 256 Boiler Control installed in our fourplex. The following are the current settings in the Tekmar:
Room occ
65
Room unocc
51
Outdr Design
-5
Terminal Unit
5
Boiler Indr
69
Boil Design
160
Boil
140
Diff
9
WWSD
47
WWSD unocc
38
Boiler trip
160
<span style="font-size:12pt">We have heating problem intermittently. The following is our observation:</span>
<span style="font-size:12pt">We have set the boiler target temperature to 45C (113F). Accordingly, the boiler flame should shut off when the boiler water reaches this temperature. However, intermittently, we note that the boiler water temperature reaches up to 65C (149F). Consequently, in such circumstance, the limit switch on the boiler trips off. Somebody at the property needs to reset it to restart the boiler to keep the heating system running.</span>
<span style="font-size:12pt">Has anybody got any idea,what is wrong in our case?</span>
Room occ
65
Room unocc
51
Outdr Design
-5
Terminal Unit
5
Boiler Indr
69
Boil Design
160
Boil
140
Diff
9
WWSD
47
WWSD unocc
38
Boiler trip
160
Settings.
What is the heating curve? What are the minimum and maximum supply temperatures? Do you have any thermostats controlling the "Demand" terminals?0 -
target vs. design
are you sure it's target temperature that you set? the only place on the control where it says target is in the display menu which is non-adjustable. to set the maximum boiler temperature (which will be establishing your heating curve) you want to set "BOIL DSG" which looks like is set for 160F and with a differential of 9F you will see the boiler hit 165.5F when it is -5F outside, so that sounds like what is happening here. what is the outdoor temperature right now and where are you located?0 -
Target vs Design
We are in Toronto and outside temperature is 23F (-5C).
Yeah, as I wrote earlier, Boiler Design is set at 160F.
Do you recommend to change any of the setting mentioned in my earlier post? If yes, what it should be in?
Thanks0 -
a couple more questions
I can give you my quick & dirty method for setting the 256 but first, what kind of emitters do you have? cast iron rads, radiant floor, baseboards etc. and what is your desired indoor air temperature? and what kind of boiler do you have? (condensing, cast iron, copper tube etc.)0 -
Emitters are cast iron rads, desired indoor air temperature is 65F and boiler have copper tubes.0 -
settings
OK, based on your info I would do these settings:
ROOM OCC = 65F
ROOM UNOCC = Doesn't matter unless you have a timer connected
OUTDR DSGN = -1F for Toronto
Terminal Unit = 5
BOIL INDR = 65F
BOIL DSGN = I'll get to that at the end
BOIL MIN = 130F to protect the boiler from flue gas condensation
BOIL DIFF = I would do 'Ad' for adjustable, and the 256 will figure it out
WWSD OCC = 65F
WWSD UNOCC = Doesn't matter unless you have a timer connected
C/F = whatever you want
Now to adjust the BOIL DSGN I would probably start at 130F and turn it up a degree a day until people stop complaining it's cold in their apt. this setting will be the maximum required system temperature at the coldest day of the year (OUTDOOR DSGN -1 for Toronto) You probably should raise the high limit on the boiler to 160F or so as well, this will be well within a safe operating range for your boiler.0 -
tekmar 256 boiler operation
The tekmar control uses a split differential. The split differential is 1/2 above target - 1/2 below target. So it will always fire above the target. The average temperature output will therefore be equal to the target.
This "Automatic Differential" can also dynamically adjust itself. The control watches how fast the boiler temperature is changing (an indication of the system load) and will get smaller or larger. If the temperature is rising rapidly this indicates a small load on the boiler. Small loads can lead to short cycling so the control will expand the differential to help prevent this from occurring.The differential is constantly adjusting every cycle.
The boiler aquastat / high limit is no longer the 'boiler control'. The settings on these should be set high enough they do not interfere with the operation of the 256 control. Set the operator at least 25°F higher than the boiler design temp entered in the 256 control. and the high limit above that. This should allow the tekmar 256 to control the boiler and prevent it from tripping on high limit.0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 55 Water Quality
- 47 Industry Classes