One-pipe Steam radiator gets hot only at top
Dot_2
Member Posts: 25
One-pipe Steam radiator gets hot only at top the bottom stays cold, i have done the following to try to resolve the problem:
Cleaned out the radiator of any sediment
Changed the air vent
Made sure it has the correct pitch to allow the condensation to drain back towards the boiler.
But still it remains the same however all others heat properly.
If I take off the air vent then it heats up on both top and bottom, I am at a lose as to how to correct this any help would be greatly appreciated.
What vent did you install?
They are not all the same, they very in size internally for different needs. Did you buy the new vent at a large box store?Cost is what you spend , value is what you get.
cell # 413-841-6726
It's a Hoffman A1 air vent that I used.0 -
Try a different vent speed
pehaps slowing it down. Also is the valve supplying the radiator fully open?Cost is what you spend , value is what you get.
cell # 413-841-6726
Yes it is fully open as I was trying to simulate what happened when the air vent was removed.
When removed it heated evenly.
I will try to slow it down to see what happens.0 -
A vent called a
Gorton C or Gorton D will vent faster the D being the fastest,Cost is what you spend , value is what you get.
cell # 413-841-6726
What is
The pressure your boiler is running at? It should be 0.5 cut in for most residential one pipe steam systems.Cost is what you spend , value is what you get.
cell # 413-841-6726
Pressure is at about 1 psi
Slowing the vent down only made a slight difference so I'll try on of those other ones.
Will update post, thanks for the advice.0 -
Cut-in
The Boiler shows the "cut-in" at 0.5 lbs while the "differential is "2.0 lbs.0