Ventrite #1
Options
drtom
Member Posts: 31
Does anyone have any experience with Ventrite #1 adjustable vents? I think I am going to use Gorton #2s for the mains, and I was thinking about using Ventrite #1s for the radiators and dialing them in for balance. Any reason not to?
There was an error rendering this rich post.
0
Comments
-
Ventrite #1
The Ventrite #1's have a range of 0.020 (setting 1)to 0.125 CFM (setting 8) at 2 oz of pressure. they will work fine but if you have a huge radiator you might want a Hoffman 1A (0.220 CFM @ 2oz - at the highest setting) for that one radiator.
the great thing about the adjustable vents is they give you a lot of leeway so you can dial in the right venting.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0