Options
heat411
Member Posts: 3
removed 80 yr old boiler, over filling! haven't installed steam boiler in 2 yrs!What should i look for?
0
Comments
-
-
by what means is it overfilling?
has it been properly skimmed/flushed etc. if the water is priming due to contaminants and it is activating the LWCO/auto-feed prematurely/unnecessariliy that would cause an overfill.
what type of LWCO installed?
what type of auto-feed?
pictures would be helpful.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
the wet returns
could well be blocked. if the water can;t get back to the boiler fast enough then the auto feeder will feed (presuming you have one). when the water does get back the boiler will be flooded0 -
yeah those are really ...
your only two options ...
in-boiler water level violent and dropping due to contaminants ..
or slow returns ..
both *may* be solved by adjusting the timing between when LW is sensed and auto-feed is activated ..
but in the case of contaminants, a thoroughly cleaning and skimming is really the PROPER means of a correction ..
slow returns may just require that the boiler start a bit overfilled to allow a buffer to catch up .. however, be wary of stacked A Dimension so that you don't stack into your mains due to slow returns
even a leak wouldn't show as an overfill.
curious .. why was the new boiler installed? something happen to the old one?1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
boiler skimming
Steam boiler. What is skimming?0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements