What causes this fireside residue?
D107
Member Posts: 1,944
4 year old Buderus G115/3, Riello 40 F3, .50 60W nozzle. Every annual tuneup there's about a good quart of powder in the chamber and baffle area. Tech came today for an unrelated minor adjustment and when i mentioned this he said it comes from not burning right. Now that we have this nozzle and pump pressure at 160 it's been running like a charm, quiet, no more impingement like we used to have with the 80 nozzles, etc. all the draft and CO2 numbers are good.
Stack temp always 325 to 350 gross. Chimney lined with stainless steel. Always get a sprinkling yellowish dust out of breech pipe on floor which I figure is condensation. I understand Firedragon's opinion is that stack temp should be 400F.
I can see how condensation(if that's the culprit) might cause the yellow/red dust in the breeching, but that wouldn't cause the reddish dust in the photo all the way in the fireside would it? happy to remove or adjust the baffles to raise temp if necessary.
I'd be surprised if the cause was improper combustion, but i've heard here and elsewhere that the boiler fireside should basically be clean upon annual inspection. It's not a big deal for the company to vac it out once a year, but figure it's better if it could run without the residue.
have you considered -
that it is a combination of a slightly low stack temp (like firedragon I would think your figures should be NETT not gross) & return water temps are on the low side. You didn't state operating conditions - so I can only speculate.0 -
Dye used in Fuel
I believe the red colored power is actually ash from the red dye used in the fuel. I have the same thing in my boiler, which is kept "at-temp" and has a gross stack temperature of about 450F.
-Rob0 -
Thanks for feedback
I didn't mention that boiler is on outdoor reset with Logomatic. It's interesting that in 2008 Buderus revised its stack temp requirements for this boiler to say: "Appoximate gross stack temp: 289degrees" for chimney vents.
Mine has an insulated liner which would be optimum but 289 seems too low. Originally it did say 350 gross, which itself was probably too low. The listed required liner diameter for this boiler is 5 inches and I'm wondering would a 4 inch liner keep the temps higher and still vent properly? it's an 18ft external chimney above the breech. Total equivalent piping length of breeching is 16.5 ft (at best should be 13.5 but that's not too bad.) Also there is no FAI but house is fairly loose mid-50s split level.
Thanks.0 -
Possible Solution: Raise Pump Logic Setting
Thanks for the photo Rick. Here's a possible solution to this problem and some I think valuable Buderus info from a very knowledgeable tech:
"I would agree that it is probably a mixture of the fuel dye and a little condensation
based on the information I read (yellow dust). The fuel dye is not normally an
issue and not much that can be done about it. If there is other residue, that
has a slight odor of sulfur or “eggs”, then it is flue gas condensation mixed
with the sulfur from the fuel. If there is a good amount of this type of
residue, the best way to clean this sulfur is with water. After the boiler is
completely vacuumed, if it’s sprayed with a little water from a spray bottle,
it just melts away (very messy job! Most technicians do not do – can’t
blame them). I have only done it to my G115 boiler once or twice in thirteen
years.
(Note: The sulfur content can vary dramatically between oil deliveries. A colleague
orders oil from the same company I do and when we tested the oil in our tanks,
there was a 100ppm difference. He is on automatic delivery, receiving oil
approximately once a month during the winter, where I normally only get a
couple deliveries a year.)
If the burner is set up correctly, check the “pump logic” on the R2107 (Can be
found in the Service level of the R2107 programming). If at the factory setting
of 104, I would increase it to 115. If the R2107 is wired properly, the “Pump
logic” will prevent the circulators from operating, only when the burner is
running. When the call for the burner to light is initiated, the R2107
“pump logic” will allow the circulators to operate if the boiler is above the
“Pump logic” setting. When the boiler is at this higher temperature there
is less chance of the return water causing flue gas condensation in the boiler.
Most technicians don’t understand how the “pump logic” works and why it’s so
important to wire the circulators into the R2107 control. If the burner is not
running, the “pump logic” does not affect the heating curve, programming or
other functions of the R2107.
I raised my pump logic setting to 115 after the first couple of years of
installing the G115 and since have had very little condensate residue.
About 2 years ago I installed the GB125BE boiler (oil fired condensing
boiler – basically the G115 with a Buderus oil burner and a heat exchanger
mounted on the rear of the boiler for the return water) as a test site and set the
pump logic at 115 from the start. I have both boilers installed and
operational in my house, but use the GB125BE exclusively. I have very little if any
condensate issues in either boiler. I fire the G115 about every other month just to
keep it on standby.
(The “pump logic” normally does not affect the domestic hot water production, as
the R2107 does not allow the circulator for the domestic hot water to operate
until the boiler temperature is above the tank temperature. This prevents the
domestic hot water loop from heating the boiler. In a standard control system
with domestic hot water, if there is a call for heat and the boiler is cold,
the cold boiler water is circulated through the indirect loop and “robs” heat
from the domestic hot water tank. This can reduce the domestic hot water output
of a tank. The R2107 domestic hot water differential is approximately 7
degrees, which normally allows adequate time for the boiler to achieve the pump
logic setting temperature before there is an effect of domestic hot water
output. The R2107 domestic hot water production feature is quite unique. It
actually “learns” the domestic hot water load over time and adjusts what the
boiler temperature needed is to satisfy the demand. It can differentiate
between a stand by temperature loss or domestic hot water usage. In the case of
a stand by loss, the R2107 will fire the boiler temperature about 25 degrees
higher than the DHW setting, then circulate the boiler water till the tank
reaches temperature.)
(Note: A Taco relay will not light up during domestic water production. Normally
if the domestic hot water circuit is wired to the Taco relay there are issues
with domestic hot water production. Such as during the R2107’s “Summer” mode
the circulators wired into the Taco relay board are not operation, so there
would be no domestic hot water during the summer time.)
The smaller nozzle, higher pump pressure is a direction that is becoming more
and more acceptable here in the United States. You are correct, about three
years ago, Buderus did its own certified testing and found the smaller nozzle
and high pump pressure did provide better combustion, less impingement issues
and cleaner combustion chambers. This theory has been used in Europe for years.
Most technicians have a preference of oil burners, mostly depended on which one
they know best, but the Riello burner still outsells the other two
manufactures combined.
I checked the stack temperatures that I have and on the G115/28 with the
Beckett NX = 410 degrees, baffles are pulled. The GB125BE22 stack temperature
has been as low as 140 degrees during a heat cycle and 180 degrees during a
typical domestic hot water production cycle (both of the boilers in my home are
direct vents). In my opinion a gross stack temperature of 289 is low for
an outside chimney. In my opinion I would look for around approximately a 350
degree, gross stack temperature with the Riello burner.
I agree trying the pump logic adjustment first, and then proceeding with
turning or pulling the baffles if not resolved."0 -
Check appendix E in NFPA 31
It being an Appendix it is not a part of the code, but you can use it as a guideline for some sizing issues. I don't have my copy handy, so cannot say for sure on the 4" change, but if you want to try it, I'd suggest using 4" pellet vent.it is Type L rated and insulated, which will give you the best chance of success in this configuration.
I have said before that when Rich Krajewski from Brookhaven put these tables out I spoke with him about them and he said that the single greatest impact on successful drfat in operation in all of his models was an insulated vent connector.
That will make pellet vent work on 4" and for 6" you could use the DS and DVL close clearance vent connector pipe fron Selkirk and DuraVent respectively. Hearthe supply is the best place to source these materials. 5" all fuel is available but check the listings. If it is tested to 103 ht it can only be used a max of 30 deg from vertical. I've been away from that business for a while but think these things have not changed.0 -
vent size
Thanks for your comment Jack. On changing the vent size I was advised:
"...I would not suggest reducing the vent size, especially with the height and distance between the boiler and chimney. A small vent size may cause other issues and may require manufacturer’s approval to meet code."
Note that the current 5" liner is insulated, but admittedly there was only room in the chimney for less than an inch of insulation all around. But I'll check out the info in your post. Thanks.0