rinniai issues
kcopp
Member Posts: 4,433
Had this one dumped in my lap... Someone else installs a 75RLSi... It was installed w/ 26 ga. smoke pipe. in a interior room.. no makeup air!
Unit was not working properly... Ran ok for a week then stops. The fix the owner would do is pull and clean the ignighter and reinstall... all is good till next week.
I am asked to figure it out.
I see the venting and demand they fix it right... which they do. I installed the proper rinniai concentric vent.(albeit it is a longer run.) ....146" and 4-90's. Looking at the install manual that is about as far as you can go...
Still locking out weekly... any thoughts?
A couple things
First throw dip switch 1 to the off position to compensate for the longer vent length. Given the method to vent I'd assume nothing is correct. Check your entering gas pressure.
Did you inspect the top of the hx when you replaced the vent? was there debris on the top of the hx fins? Drop the inducer motor and look up inside to see if the combustion air diffuser is clean. Make sure when you do so that you re-insert the tab on the inducer and then lift it into position. I've had guys miss that and the back of the motor hangs and the unit is not happy. I'd order a new sparker flame rod and gasket just to get back to square one.
Rinnai's number is 800 621-9419. Call them from the job and they will walk you through the checks. Where are you located?
Finally, do look up the original installer and...%&(*%#$.0 -
Thanks...
I am in New Hampshire. Unit is is a Salon... they have to have reilable hot water.0 -
Fuel
Are you even sure it is using the right fuel?0 -
I'm your rep...call me
617 834-8751. Tues am?0
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements
