Triple acting relay
TonyS
Member Posts: 849
After removing a tankless coil and installing a separate water heater how do you turn the triple acting into a cold start relay?
low limit
turn the low limit setting all the way down.....or put in a regular aquastat relay.......paul sASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Depends what make...
I have a Honeywell Triple Acting Relay. I found the lead wire for the low limit setting and disconnected it (simple spade connector). If you find the wiring schematics, you can find the right wire, or post a model number for the relay and we'll find something.0 -
L8124a
I traced out the board and it looks as though eliminating the red wire feeding the bottom of the low limit should be disconnected and capped, then the circulator is now run off of ZR and the burner remains on B1. ZR AND B1 are now only energized when TT is complete but the burner still cycles on the high limit. Does this appear correct?0 -
no that's not the correct wire to disconnect
That's not it0 -
I have the same Aquastat.
Disconnect the blue wire going to terminal B right next to the Differential dial. It's just a stake-on connector that you can pull off. Don't cut any wires.0 -
I set one up today
If you disconnect the red wire feeding in just below the low limit and cap it(wirenut) that is the only feed that remains hot after the relay is deenergized. The problem is that the circulater terminals are charged off that wire. The high limit side is independent and has its own built in 10 degree differential. The ZR terminal is only energized when the relay is energized as is the B1 terminal except the B1 terminal can be interupted by the high limit. By using the ZR terminal for the circulator, the circulator will be energized whenever the relay is energized(TT call for heat) and the high temp switch will operate the burner but will also drop out whenever the relay is deenergized.0 -
I am going to try
removing just the blue wire tommorow. Thanks0 -
Cold Start
See I wouldn't make it a cold start ... I would maintain enough temperature to prevent combustion condensing and seal leakage . Drop it down to 120 .. Most coiled boilers are not designed to be cold start like a Buderus ... Even the Buderus Logamatic controls let's the boiler build a little until it powers up the heat zones ...I have enough experience to know , that I dont know it all0 -
Blue wire removed as shown with red box in picture.
Follow the wires now and you'll see that everything works the way it should in a high limit aquastat.0 -
These same boilers
most of them New Yorkers come with a cold start relay when you order them without the coil. After installing a water heater the customers sure dont want to hear that oil burner start again till next winter and just turning the triple acting down doesnt stop it from running.0
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 129 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
