How to size an RPZ / Backflow Preventer?
Jason Quinn
Member Posts: 96
When used in hydronics, is an RPZ size based on the connected BTU's of the boilers,system pressure, something else? Does anyone have a reference I may use? Thanks in advance.
Size it to....
the required flow. 1/2" is typical for a residential system.
If you don't make a solid connection between the potable water and the non potable space heating water, you don't need any protection required by code (sill/drain cocks).
That will also avoid long term unseen water damage.
Make sure you have low water and or low pressure cut offs.
ME0 -
Thanks, ME
By required flow, do you mean the flow of the heating system or the flow required to fill the system?0 -
RPZ
I think Mark is saying the required flow needed at the point of connection. Operating parameters of both sides of the RPZ/backflow device must be considered as well. Check the specifications of the device and compare it to the installation.
Most boilers will only need a 1/2" line for make-up. Can't think of the last 3/4" or larger RPZ I tested/serviced connected to a boiler. The larger boilers I see are usually in churches and apartment buildings though.There was an error rendering this rich post.
- 119 Chimneys & Flues
- 116 Geothermal
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam
