How to size an RPZ / Backflow Preventer?

Jason Quinn
Jason Quinn Member Posts: 96
When used in hydronics, is an RPZ size based on the connected BTU's of the boilers,system pressure, something else?  Does anyone have a reference I may use?  Thanks in advance. 

Comments

  • Mark Eatherton
    Mark Eatherton Member Posts: 5,866
    Size it to....

    the required flow. 1/2" is typical for a residential system.



    If you don't make a solid connection between the potable water and the non potable space heating water, you don't need any protection required by code (sill/drain cocks).



    That will also avoid long term unseen water damage.



    Make sure you have low water and or low pressure cut offs.



    ME
  • Jason Quinn
    Jason Quinn Member Posts: 96
    Thanks, ME

    By required flow, do you mean the flow of the heating system or the flow required to fill the system?
  • EricAune
    EricAune Member Posts: 432
    RPZ

    I think Mark is saying the required flow needed at the point of connection.  Operating parameters of both sides of the RPZ/backflow device must be considered as well.  Check the specifications of the device and compare it to the installation.



    Most boilers will only need a 1/2" line for make-up.  Can't think of the last 3/4" or larger RPZ I tested/serviced connected to a boiler.  The larger boilers I see are usually in churches and apartment buildings though. 