Which vaporstat
Luv'nsteam
Member Posts: 278
In looking up a part number for the Honeywell vaporstat, L408J, I see there are two sub numbers. One has a SPST switch (L408J1025) and the other has a SPDT (L408J1009). I didn't notice any other differences (are there?).
For my one-pipe vapor steam heating system, which one do I want?
Thank you,
Mike
Thank you,
Mike
L408J Vaporstats
Hi Mike- Here's some info on Vaporstats for you.
- Rod0 -
Vaporstat choice
Hi Rod, thanks for the PDF's. After looking at them, I think I want the SPDT vaporstat. I think this because the vaporstat, LWCO (float) and LWCO (probe) will be wired in series. The L408J1009 has the SPDT switch and breaks contacts R/B on rise, where the SPST only makes on rise. SInce I am using the vaportstat to shutdown the boiler on pressure rise, and only the 1009 vaporstat breaks on rise, this is the model I want, correct?
Thank you,
Mike0 -
Yup
you'd use the other one to shut off the burner if the pressure fell. The 1009 is the one you want.All Steamed Up, Inc.
Consulting0 -
Much appreciated
Steamhead and Rod, many thanks to both of you for your help.
Have a great week,
Mike0