heat pump won't run
john0970
Member Posts: 4
I am dealing with a 2 ton Advanced Air heat pump. The outdoor unit will not run. It is getting high and low voltage. I pressed the contactor and the fan started. The led troubleshooting codes are telling me that everything is fine. The compressor does not hum. I am thinking that it is in the control board. I'm not sure if i'm right though. The indoor unit does run properly.
low or high pressure switch?
blocked air filter will trip high pressure switch in the heating mode.
you say its getting 24v but is it calling,, is there a pan switch, or an overflow switch on the condensate pump.
look for any manual reset type switch on any pipe inside the condensing unit.There was an error rendering this rich post.
reply
there is no condensate pump....condensate is piped directly outside. The l.e.d lights on the outdoor unit do not show a high or low pressure problem.0 -
check to be certain it is calling for heat
by what your saying I'd be looking hard at that,
make sure its not in the emergency heat mode
does the board have an indicator that it is indeed calling for heatThere was an error rendering this rich post.
no emergency heat
unit does not have emergency heat. unit is 3 years old and the indoor unit comes on when it calls for heat.0 -
h-p won't run
just how far are you getting 24v?0 -
Sounds like...
If you have both line voltage and low voltage at the outdoor unit, it sounds like you have either an open pressure switch or a defective contactor coil.
You mentioned that the outdoor fan operated when you manually pushed in the armature on the contactor, so your line voltage power circuit seems to be intact.
You should take a voltage reading across the contactor coil on a call for heat and determine if you indeed have 24 volts at the coil. If you have low voltage at the coil, the coil is defective and the contactor needs to be replaced.
If there is not voltage across the coil, it is likely that there is an open pressure switch. On many heat pump systems, the pressure switch is the only safety/operational device in series with the contactor coil at the outdoor unit. The common side of the coil often retrns to the indoor unit via a common terminal connection on the defrist control.
Keep us posted.0 -
new contactor and reset low pressure
i installed a new contactor and reset the low pressure switch. maybe it's not getting a call for heat. i checked all the low voltage connections in the indoor unit. maybe it's the t-stat? this is driving me crazy...lol0 -
Heat Pump
What mfg makes this H.P.?At the outdoor unit ,with the system calling 4 heat,do u have 24v on the common and heating{hot} wire? Is the 24v side of the xformer grounded?If yes, put 1 probe 2 ground and the other probe to the heating [hot] wire .You should have 24v.Then hopscotch thru the switches to the hot side of the contactor.Do u have 24v all the way?If yes, put the 2nd probe on the common side of the contactor,do u have 24v there?If yes then ur common leg is open somewhere, or both 24v legs are the same leg.0 -
John:
Can you provide a wiring diagram? I'm sure one of us can help you through it. From what you are telling us, one of the safeties must be open. Step back for a while and trouble shoot from the contactor back if you can.
Mike T.0 -
Have you...
....ohmed out the compressor to make sure it's still working? Does it work in cooling mode?0
- 87.7K THE MAIN WALL
- 127 Chimneys & Flues
- 121 Geothermal
- 79 Pipe Deterioration
- 396 Solar