Taco 571-2 Zone Valve Issue
Options
bisquits1
Posts: 7
I have a Taco 571-2 Zone valve that seems to be malfunctioning. The zone control is lit red for Zone 2 and there is no flow of hot water. If I switch the valve to manual, I do get flow. Is it possible that just the head of the valve is bad??? By twisting the valve to remove the head, will there be any water loss??
0
Comments
-
the head is...
replaceable w/o the water loss. Wait for the call for heat to be off before doing that allowing the piston to cool.0 -
Taco 571-2
Thanks for the info, waiting for Grundfos to come out with Zone Valves so I can try one of those ALPHA ECM pumps. Old system, but trying to make it more efficient.0 -
manual vs auto
If I switch the valve to manual, will the zone continue to just run?? Probably not too good on the overall run time of the boiler??0