I used siggy's equation
Options
MikeJ
Member Posts: 103
to come up with the buffer tank size, that equation does not compestate for the boiler modulating. I would think if any one had a equation to compensate for the modulating. It would be siggy. I have some his books but could not fine a equation for it. What I want to do it calls for a 80 gallon tank according to the equation. But by gut feeling (plus NRT_Rob post) is saying a 30 would suffice,
As far a buffer tank size, too big shouldn’t be a problem.
Plus with the Ramp delay, gradient limiting. You would think you could get a min 10 minute run time with a 30 gallon buffer tank.
As far a buffer tank size, too big shouldn’t be a problem.
Plus with the Ramp delay, gradient limiting. You would think you could get a min 10 minute run time with a 30 gallon buffer tank.
0
Comments
-
try these
Just rearrange the terms. Play with them in Excel.
To get a runtime based on various inputs, use
t = (Vbt*500*dT) / (Qh - qload)
To get the input (modulation) required for a given load, runtime, dT, and buffer size, use
Qh = ( (Vbt*500*dT) / t ) + qload
For example, you want to know the modulation that gives a 10 minute runtime with a 30 gal buffer, 20 dT and load of 10000 BTU/hr.
Qh = ((30*500*20)/10) + 10000
Qh = 40,000 BTU/hr
Say you want to double the runtime. Now the modulation is down to 25k BTU/hr.
There's not a simple way I can think of to model a continuously modulating input, but do enough playing in excel and you will see what changing the variables does and hopefully find your answer.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 428 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 76 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements