Problem with Caleffi manifold
John Owens
Member Posts: 5
I am getting bleed through on a project with three Caleffi manifolds. All the telestats are closed, and I can see visible flow on at least three flow indicators when another zone is calling for heat. I have set hundreds of manifolds in the last 20 plus years, Infloor, Stadler, Rehau, Wirsbo. I removed and reinstalled the telestats, and then installed three new telestats to no avail. I suspect a problem internally withe valve stem in the manifold. Has anyone had a similar experience.
I'm anticipating the " That's the first time we heard of that" conversation, Any help would be appreciated.
John Owens
John Owens
System fluid clean?
Had a similar problem on a lesser quality manifold. I had to remove the manifold and clean it because the valve assembly was corroded due to poor maintenance of the system glycol.There was an error rendering this rich post.
which manifold
are you using? And which operator?
If you remove the operator and screw the white cap on, does the flow stop. That would tell if something is stuck in the valve seat and help narrow down the problem to the valve or seat. Or if the operator is the issue.
hrBob "hot rod" Rohr
Living the hydronic dream0
- 50 Industry Classes