Different pressuretrols types?
RyanC
Member Posts: 38
I have a PA404A 1033 pressuretrol. What is the difference between the PA404A 1033, 1025, 1092?
Thanks,
Ryan
Thanks,
Ryan
Perhaps this will help ..
PA404A PRESSURETROL. MAKES CIRCUIT AT SETPOINT PRESSURE FALL; BREAKS AT SETPOINT & DIFF. ON PRESSURE RISE. ADJ ADDITIVE DIFF: 1-5 PSI. SAFETY FOR STEAM HTG BOILERS.
PA404A1025 PRESSURETROL SPST SWITCHING. BREAKS ON PRESS RISE. RANGE 3 TO 15 PSI. RANGE .2 TO 1.0 KG/CM2. SUBTRACTIVE DIFF. 1 180.55 12 0.8 0003 GEN
http://customer.honeywell.com/honeywell/ProductInfo.aspx/PA404A1025
PA404A1033 RANGE .5 TO 9PSI (.1 TO .6KG/CM2) WITHOUT LUGS TRADELINE
http://customer.honeywell.com/honeywell/ProductInfo.aspx/PA404A1033
I couldn't find a 1092 reference.
Additionally, here is the brochure for all Honeywell Pressure controls.
http://customer.honeywell.com/techlit/pdf/63-0000s/63-9727.pdf1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0