Type and Size Steam trap
Big Ed_4
Big Ed_4 Member Posts: 3,209
I am installing twin 630k Fulton boilers 120# steam system. Running a 1.25" main  40'. What type and size trap should I use on the end of the main on the drip leg ?  Thank for any info ..
Ed
  • Big Ed_4
    edited September 2009
    No sure if posted correctly
    Two 630 Futons 120# steam boilers. Running 1.25" main 40' , what type and size trap should I use on the end of the main drip leg.?Thanks again
  • kevinj_4
    kevinj_4 Member Posts: 91
    Trap
    More info wioll be needed to size the trap. If you contact your Sarco or Armstrong rep they can size it. It will be about the smallest trap you can get.
  • joe lambert_2
    joe lambert_2 Member Posts: 61
    Small is Correct
    I like using Float & Thermostatic traps these days, they are good at removing air that you will have on start-up.  You could use a 3/4" or 1" F&T-125 trap.  Make sure you get the orifice for 125 psi steam.
    I have seen some large traps on the main headers for boiler, these are there in case there is carry-over of boiler water into the steam line.  I don't usually recommend them but prefer to prevent carry-over at all costs.
  • kevinj_4
    Tiny boilers
    These must be real small to only need a 1.25" main.
