Ray Boilers with Indirect
Options
FT
Posts: 3
Recent conversion from oil to gas with 2 Ray Boilers & 1 Indirect for a 6 family house. Can't have the boilers isolate the power to the indirect till late June (updated version coming from the factory)so we installed an Argo 2 zone relay. People are complaning to hot so as a result the windows remain open in some Apt's. Our biggest issue is that the boilers don't start for Hot Water usage...
Any similar issues??
Any similar issues??
0
Comments
-
Check your control wiring. All of my Ray installs have indirects and they call the boilers to high fire. Your heating zones and indirect should be completely independant of eachother. Indirect calls to its own terminals and the zones signal to the IAR strip.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0