CONVERSION BURNER
Options
bob young
Posts: 2,177
When using a conversion gas burner w/ a barometric is a draft diveror necessary . can you sustitute a divertor & delete the barometric
0
Comments
-
Sorry
Scrook is correct a double acting barometric0 -
thanks ROBERT , for clarifying that for me.0 -
wouldn't it...
it be/require a double acting (gas type) barometric, not a draft diverter for a gas power burner/conversion burner?
Always learning.0 -
Draft diverter
is not necessary. The double acting barometric will work much better than a draft hood.0 -
THANKS AGAIN , GENTS
Hope you are feeling up to snuff ,Tim.0 -
Thanks Bob,
I am feeling great!0