Steam coils
nugs
Member Posts: 77
No numbers or manufacturers stamp? If you can find any of those you should be able to look it up.
Steam heating coils
I am sizing up a replacement steam boiler. The system has a steam coil in the duct work. How can I find the EDR rating of the coil?
Frank's method with no rating plate visable
or use Frank's alternate method. highest btu rating for supply pipe size of coil0 -
Use...
... the CFM of the fan, and the delta-T of the air. That'll tell you how many BTU/hr or lbs/hr steam the coil requires.
Heating air with steam:
(CFM X 1.08 X delta T in *F) / 1000 = lbs/hr steam0